Tripped Breaker On A/c - HVAC - DIY Chatroom Home Improvement Forum
Old 06-12-2008, 11:31 AM   #1
tripped breaker on a/c
i just installed a 1200 btu mr slim,it ran fine for one day ,then started to trip the 20 amp breaker,it did this for 2 days then it ran fine after that.the weather was in the 90s anyone have this problem before,any thanks for any help.also i checked all the elect. fittings they were all tight.
bob p. is offline   Reply With Quote
Old 06-12-2008, 04:31 PM   #2
Electrician
That has a indoor and outdoor unit correct? Anyway what are the nameplate ratings on the equipment...
chris75 is offline   Reply With Quote
Old 06-16-2008, 10:39 AM   #3
mr slim
inside 120 volts phase 1 60hz
outside 120volts phase 1 60 hz max volt 127 ampicity 16
Old 06-16-2008, 08:50 PM   #4
possible triping of the breaker on start up. Most units will momentarily start at higher amps on start up....20 A should have a minimum of 12 guage wire between the unit and panel..if it is a long distance (25' or more) then I would recommend installing 10 gauge wire to assist in the power loss.
statman is offline   Reply With Quote
Old 06-16-2008, 08:54 PM   #5
Electrician
Thats not the problem, what would a bigger gauge wire do in stopping the breaker from tripping? I think the OP has the outdoor and indoor unit on the same breaker.
Old 06-17-2008, 07:36 AM   #6
Some Mr. Slim ductless splits I have worked on will communicate with each other and can be wired separately or together. 20 amps does not seem out of whack for a small unit and it would seem that the unit is slightly overamping on startup. Power loss through a distance of wire will cause this,,...increasing the wire size reduces the power loss, if in fact this is the case.
Old 06-17-2008, 07:44 AM   #7
mr slim tripped breaker
it has approx. 50feet of #12 wire,both units are on the same breaker thats how this unit is made.the unit would run for approx.3-4 min. before it trips,it has not tripped since the 90 degree weather is gone. i am not on the computer sometimes for a day or two,but i will be back tosee any replies.
thanks bob p.
Help! Circuit broken but breaker isn't tripped kevind Electrical 3 01-19-2008 06:13 PM
20 Amp Breaker tripping with GFCI panhandlion Electrical 7 12-12-2007 09:59 PM
Breaker Buzz SkipI Electrical 2 07-13-2007 08:48 PM
Breaker tripped again rookie50 HVAC 8 12-02-2006 06:57 PM
tripped breaker rookie50 HVAC 7 11-28-2006 03:40 PM