I have read the posts by Tom Scott and others having the dreaded 3 red light pressure switch error. I have the same problem. Furnace runs fine with the vacuum tube from the pressure switch to the burner box disconnected, so we don't freeze at night, but of course that's not a safe long term solution!
I've cleaned all of the vacuum tube lines, nipples and connections. I've checked and cleaned the condensate line from the inducer motor and from the heat exchanger area of the furnace. I've checked that the air intake and exhaust pvc ducts are clean and clear. I've even replaced the pressure switch (twice!) and the inducer motor, which had some stains on the underside, indicating possible overheating, I thought.
After all of this, I still had the problem, so I called the local Trane dealer.
The Trane repairman spent about an hour testing and diagnosing the problem. Checking pressures and such. He discovered that if you plug the end of the condensate drain line coming from the furnace (not the line from the inducer motor), the pressure switch error goes away. He thinks the problem may be with the condensate drain trap, which is not set up properly, he says.
As you can see (I hope!) in this picture, the condensate drain lines from the inducer motor and from the heat exchanger are simply routed into a pvc drain pipe with a gravity trap built into it, like under a sink.
The pressure switch error (3 red lights) goes away if you plug the end of the condensate line that comes from the furnace (not the line that comes from the inducer motor). Repairman says Trane makes a condensate drain trap that should have been installed when the furnace was originally installed in 2003.
Note that the drain line that comes from the furnace does not extend all the way down to the bottom of the pvc trap, where it would be submerged in a bit of water. It only extends a few inches into the pvc pipe, so that air can flow backward through the condensate line into the furnace heat exchanger area right next to the vacuum line that goes to the back of the pressure switch, reducing the relative low pressure in the furnace at the heat exchanger area.
Does a faulty condensate drain trap sound like a correct diagnosis?
Does the the Trane condensate trap actually prevent air from flowing back into the furnace? If so, then problem solved.
Should not be complicated to install the trap. However, I went to the Trane site and discovered that they do not sell direct to the public. Is there anywhere that I can purchase the Trane condensate trap and the appropriate size tubing (as existing lines undoubtedly will not be long enough)?
Of course, if the Trane condensate trap allows air to flow back into the furnace heat exchange area, then problem is not solved, and all that is left is to conclude that the heat exchanger (or transition piece to inducer motor) must have cracks, as many others have had.
Thanks for any advice you may be able to provide.
JD
JD