Trane XR13 Help - HVAC - DIY Chatroom Home Improvement Forum
Old 06-28-2010, 01:01 PM   #1
Trane XR13 help
Hello,
I got a Trane XR13 AC compressor installed in June 2007. The unit will not come on now..either the Compressor nor fan will run. No humming sound.
I checked the circuit breaker and its fine.
I tested the Run Capacitor with my multimeter and got 5uf on the fan side...38uf on the HERM side. The capacitor rating is 5uf/40uf.
Any ideas/suggestions?
moxcoyote is offline   Reply With Quote
Old 06-28-2010, 04:51 PM   #2
Do you have 240 volts at the contactor? Have 24 volts going out to the unit? High pressure switch tripped?
Old 06-28-2010, 08:46 PM   #3
I was able to resolve the issue. Wasn't getting 240V on the contactor. The panel at the side of the house had a blown 20A fuse in the box where the power was coming out of the house to the outdoor unit. Replaced the fuse and compressor/fan works fine.
Old 06-28-2010, 09:09 PM   #4
Hvac Pro
yuri's Avatar
Rewards Points: 150
Use "time delay" fuses and not the general purpose cheaper ones. Those are for lights etc. Motors need time delay fuses. Usually about $3-5 apiece but worth it.
Old 06-28-2010, 09:36 PM   #5
Thanks Yuri...Those are the ones I ended up replacing them with. 8.00 for a pack of 2.
Ruud vs Trane peter_holmes HVAC 23 07-28-2010 02:32 PM
Need some friendly advice-- Coleman/York v. Trane biggerdaddynj HVAC 3 05-09-2010 10:46 AM
new install of Trane XL15i nind HVAC 32 01-30-2010 12:59 PM
Trane Heat Pump acting up..frozen (XR13) VEIK HVAC 1 10-20-2008 03:00 PM
Air handler for TRANE XR13 alex333 HVAC 1 07-09-2008 03:23 PM