Trane XL90 Highlimit Switch Open - HVAC - DIY Chatroom Home Improvement Forum
Old 01-18-2013, 07:21 AM   #1
Two Trane 90XL installed 2000 run off one thermostat. One runs great now. Second furnace blows cold air and burners have no flame.
First service tech said problem was drain tube loose and pressure set too high.
Adjusted pressure and cleaned drain tube and reservoir. Same thing happened again in 3 days.
Second tech says that the main board is shot because the 4 light pulses indicate the high limit switch is malfunctioning. He jumped the high limit and the furnace started normally then quit.
He says the board is shot and needs replaced.
Can any one confirm his diagnosis?
burger19 is offline   Reply With Quote
Old 01-18-2013, 07:32 AM   #2
AKA HVACTECHFW
Rewards Points: 1,208
No, board is not shot. You have an airflow issue. (blocked supply vents, blocked returns, plugged filter, plugged evap orator coil, plugged secondary heat exchanger coil, weak blower motor, inoperative blower motor, or weak blower motor capacitor) First thing to do is identify why the main limit is tripping, then if the limit is sticking closed you should replace the limit.
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 01-18-2013, 11:20 AM   #3
I think I jumped the high limit
Thanks for your response.
I took off the cover to expose burners but did not pull them and to access the high limit switch in the ex changer chamber.
The wire were in a connector. I put a small wire into the connector and turned the furnace back on. There was a zap noise and I had to reset the breaker.
After resetting the breaker the furnace came back on and the error code blinked 9 times. I checked the on the door of the furnace 9 blinks check ignition.
I checked several times and confirmed there are now 9 blinks instead of the 4 blinks.
The furnace still blows cold air. I checked and there are blocked supply or returns.
What do you think?
Old 01-18-2013, 12:29 PM   #4
AKA HVACTECHFW
You have likely ruined your control board by shorting it out
IT IS WHAT IT IS
Old 01-19-2013, 07:38 PM   #5
Furnace now running
The furnace i now running I must have some how reset the high liit switch. I laso mad e sure there was nothing blocking supply and returns.
However, the flame is not bue like the first furnace it is amber yellow.
What is missing, thanks.
Old 01-19-2013, 09:05 PM   #6
An old Tradesmen
Rewards Points: 6,464
Is the inducer running.
Old 01-19-2013, 09:18 PM   #7
Inducer Running
The inducer was running previously .When I returned to the property I really only felt the heat and looked in the heat exchanger through the see through window to see the amber fame. I initially thought the board was blown so seeing it working was a relief.
Things seem to be normal but there was not a strong air low at the affected vents.
Is there a serious problem if the inducer is not running?
Will the furnace be destroyed?
Old 01-19-2013, 09:27 PM   #8
An old Tradesmen
Shouldn't even be able to light the gas without the inducer running. but you shorted something out. So no telling what may happen. It need attention.
Old 01-19-2013, 09:31 PM   #9
How serious is this? Can it wait until tomorrow? What do you suggest?
Old 01-19-2013, 09:33 PM   #10
An old Tradesmen
I'd shut it off. You could be sooting up he secondary heat exchange. No telling if the safeties work now.
The Following User Says Thank You to beenthere For This Useful Post:
burger19 (01-19-2013)
Old 01-19-2013, 11:12 PM   #11
Okay I shut it down. I'll get serviceman tomorrow or Monday. Other furnace running well.
Thanks for the info. safety First Always.
Old 01-19-2013, 11:28 PM   #12
An old Tradesmen
Good decision.
Diagram for 3 way ceiling fan light switch Aurora65 Electrical 22 11-27-2012 10:11 AM
3 way switch layout has me confused crescere Electrical 5 09-08-2012 11:26 AM
safety overflow switch trane xl14i jeffrey sehl HVAC 2 08-10-2012 11:15 AM
can switch work for two different outlets? jlmran Electrical 8 02-10-2011 01:31 PM
Basic Switch wiring question; Dimmer to Toggle switch (Pictures included) inspectator Electrical 8 08-07-2007 02:19 AM