-   -   Trane XL1200 - Outdoor Unit Problem (http://www.diychatroom.com/f17/trane-xl1200-outdoor-unit-problem-21711/)
snifred81 06-01-2008 11:38 AM
We have a Trane XL 1200 Heat Pump. The unit was installed in 1999, we bought the house in 2005. The cooling coil died right before we moved in and was replaced in Aug '05. In the summer of '06, when we first changed from heat to cooling, it wouldn't come on. Turned out it was tripping the breaker. So last year, we turned the whole system off for about 6 hours before trying the cool setting, and everything was fine.
This week, when we tried to put the AC on, the outdoor unit does not start. The thermostat symbols show that the cooling is on, but the air is not cold enough to cool the house since the outdoor unit isn't on.
We have tried resetting the breakers for both the indoor and outdoor units, and turning the whole system off and then back on. Still nothing.
Any ideas?
Thanks!
wirenut1110 06-01-2008 12:18 PM
By what you're saying it sounds like the contactor on the condensing unit has failed possibly a burnt coil on the contactor.
BillyD 06-02-2008 06:19 AM
Good luck. The worst heat/cool unit I ever owned was a Trane. It hard to stop a train because you can't get it started. Ours worked great for 3 years then it was something every year.
RTG Service 08-07-2012 10:21 AM
Check for 24VAC at the contactor coil, if you don't check the transformer output and the Y circuit coming from the thermostat.
As for popping the breaker it could be a number of things.
My advice would be to start with one problem at a time and yours would be to figure out why you are not getting you contactor to close.
:thumbup:
wirenut1110 08-07-2012 01:45 PM
This thread is only over 3 years old. If it's not fixed by now, he doesn't need it.:eek:
RTG Service 08-07-2012 01:53 PM
I am a newby and just realized the posting date...thanks.