Trane xe80 no heat


Hello, I have a 10-11 year old Trane XE80 unit mounted horizontally in my attic. I replaced 'stat with a Honeywell 6110 sometime this past year and this is the first time I've had to fire up heat. (Cooling worked fine over the summer). I'm sure I wired it up right when I installed, but I'm getting no heat. Done alot of reading and here's where I'm at:

I unscrewed all 'stat wires from furnace board (left A/C compressor wires in place), jumped the red and black to fire heat. I get blower motor and 9 blinks - "Check Ignitor". So I pull the HSI where I can see it, fire up the routine again. I can see a bit of red but I don't think it's hot enough to fire gas. I am getting no gas smell between tries, but that may be indication that gas valve doesn't start until system verifies the ignitor is working???

So I figure it's worth a try given that the system gave me the check ignitor code. I have an, I think, obsolete Trane B340971 in it. My Trane dealer had an IGN00117 as the replacement. I haven't mounted it yet, but when I run the same test, jumping the R/W with the ignitor pulled out within view, I get the same 9 flash code. Will I have to mount it to get best test results?

Should I rehook the stat and test it completely reassembled?
Should I pull the flame sensor and clean it off while I'm in there?
Should I be able to mount new ignitor without pulling the whole venturi tube assembly?

Any other suggestions to look at before I have to make a call?

tackman is offline   Reply With Quote
Old 11-04-2010, 06:42 PM   #2
Newbie
 
Join Date: Nov 2010
Posts: 6
Default

Trane xe80 no heat


Update: new Ignitor, correctly mounted in-place not firing up either. I remove it from its bracket and view it and it gets no redder than previous. (OK, so I may have a good spare now). But what could be preventing ignitor from getting fully hot? Is there something in the system I can check that is preventing sufficient time or current for ignitor to be heating up?

Old voltmeter, see pic:



...will register about a 5 on the bottom scale when set on 250. While I'm not sure if I'm reading it right, I figure that's 5 out of 10 or 1/2 of 250 or about 120 volts being fed to the ignitor. But it only stays there for about 1.5 seconds and then power to it shuts off, the fan stays on and the 9-flash code comes on. So I think the correct current is getting to it, I just don't think that it's allowing it to stay on long enough.

Any ideas or help?

tackman is offline   Reply With Quote
Old 11-04-2010, 08:09 PM   #3
HVAC / Plumbing
 
Join Date: Feb 2009
Posts: 1,801
Default

Trane xe80 no heat


Most furnaces get power for heat to come on from the white wire. You are saying yours is powered with lack wire ? at the control board. r w g y c
kenmac is offline   Reply With Quote
Old 11-04-2010, 08:12 PM   #4
Newbie
 
Join Date: Nov 2010
Posts: 6
Default

Trane xe80 no heat


Sorry, mistyped that. I cross the red and white (hey I did get it right later with the R/W!)
tackman is offline   Reply With Quote
Old 11-04-2010, 08:13 PM   #5
HVAC / Plumbing
 
Join Date: Feb 2009
Posts: 1,801
Default

Trane xe80 no heat


so did you check voltage ?? should get atleast 24v from w to c
kenmac is offline   Reply With Quote
Old 11-04-2010, 09:54 PM   #6
Newbie
 
Join Date: Nov 2010
Posts: 6
Default

Trane xe80 no heat


I just did check it and I am getting 120v to the board on the line spades, and (again, I think,) better than 24 v from w to c. So is transformer working? Bad board (50A65-475)???
tackman is offline   Reply With Quote
Old 11-05-2010, 01:03 PM   #7
HVAC / Plumbing
 
Join Date: Feb 2009
Posts: 1,801
Default

Trane xe80 no heat


If you are getting 110v where the ignitor connects to the board on a call for heat & ignitor doesn't glow. Then, ignitor is bad. If you don't have 110 where ignitor connects to board & all other functions are ok.then, board is bad

Last edited by kenmac; 11-05-2010 at 01:11 PM.
kenmac is offline   Reply With Quote
Old 11-05-2010, 01:11 PM   #8
Newbie
 
Join Date: Nov 2010
Posts: 6
Default

Trane xe80 no heat


The 120v I said I was getting at the board was testing the Line-In hot and neutral.

I didn't test at the board where the ignitor plugs in during a call for heat. However I did test at the modular in-wire plug during call for heat and got 120v. So 120 must be leaving the board, but only for about a second and a half.
tackman is offline   Reply With Quote
Old 11-05-2010, 01:30 PM   #9
HVAC / Plumbing
 
Join Date: Feb 2009
Posts: 1,801
Default

Trane xe80 no heat


I've never timed it. It must have 110 long enough to glow the ignitor up to temp
kenmac is offline   Reply With Quote
Old 11-05-2010, 01:33 PM   #10
Newbie
 
Join Date: Nov 2010
Posts: 6
Default

Trane xe80 no heat


It's def not staying on long enough. Don't know what else to look at at this point besides blaming the board and I hate to make that assumption so fast.

tackman is offline   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help me compare Trane heat pumps pls tomseeley HVAC 3 04-02-2010 05:54 PM
Trane Aux heat modification tj1mcd HVAC 2 12-05-2009 07:24 PM
Trane Heat Pump Not Blowing Cold JbIcon HVAC 3 09-01-2009 10:15 AM
trane x19i heat pump MrSnapRon HVAC 8 08-29-2009 01:17 PM
Are Trane heat pumps and Am Std exactly the same? jgtaylorjr HVAC 1 06-01-2008 09:35 PM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.