Trane XE1000 compressor not coming on line.


I have a Trane XE1000. Believe the compressor is not coming on line. The out door fan is coming on line. What is the best way to determine if power is getting to the compressor?

While I had some one turning the system on and off from the thermostat, I was watching the contactor switch. It was closing and the fan world come on when the switch closed. A few times the switch did not close. Can the switch fail in such a way that the fan receives power but the compressor does not receive power?
Thank you,
Flathead64 is offline   Reply With Quote
Old 10-26-2009, 12:31 PM   #2
Member
 
Join Date: Nov 2006
Posts: 291
Default

Trane XE1000 compressor not coming on line.


You probably need to get the wiring diagram for this specific unit.

In general when the contactor closes it energizes the run winding of both the compressor and fan motor. If the compressor is not comming on then it's internal overload switch could be open or it's run capacitor is faulty.

The fan comming on "generally" suggests the contactor is OK. However the starting surge required by the compressor is much larger then the fan motor so I guess the contacts could be marginal.

Be careful. Do all your initial diagnostics with low voltage only. Pull the 220v disconnect until you absolutely need the high voltage.
hennyh is offline   Reply With Quote
Old 10-26-2009, 09:55 PM   #3
Member
 
Houston204's Avatar
 
Join Date: Oct 2009
Location: Texas
Posts: 585
Default

Trane XE1000 compressor not coming on line.


Is this a heatpump or condenser?



Houston204 is offline   Reply With Quote
Old 10-27-2009, 06:59 AM   #4
Newbie
 
Join Date: Jun 2009
Posts: 7
Default

Trane XE1000 compressor not coming on line.


It is the compressor located in the outdoor unit.
Flathead64 is offline   Reply With Quote
Old 10-27-2009, 08:46 AM   #5
Member
 
Join Date: Nov 2006
Posts: 291
Default

Trane XE1000 compressor not coming on line.


That schematic clearly shows that the contactor energizes the run winding of both fan motor and compressor. If fan runs and compressor doesn't then I stand by my earlier suggestion to look at run capacitor, compressor overload, wiring or maybe a flakey contactor. (in that order)

Capacitor failures are very common.

Does your unit have the start kit?? Sometimes it's only an option for certain applications.

Last edited by hennyh; 10-27-2009 at 08:50 AM.
hennyh is offline   Reply With Quote
Old 10-27-2009, 08:07 PM   #6
Member
 
Join Date: Oct 2009
Posts: 67
Default

Trane XE1000 compressor not coming on line.


probably the compressor run capacitor is dead
mrairflow is offline   Reply With Quote
Old 11-03-2009, 07:53 AM   #7
Newbie
 
Join Date: Jun 2009
Posts: 7
Default

Trane XE1000 compressor not coming on line.


Thank you for all of the help. Iíve learned quite a bit. However, I could not ID the problem so I punted and brought in a service technician. The 59 cent guts of the Schrader valve had failed and nearly all of my R-22 had left to burn a hole in the atmosphere via my wallet.
Thanks again for your time and efforts!
Flathead64 is offline   Reply With Quote
Old 11-03-2009, 08:27 AM   #8
Member
 
Join Date: Nov 2006
Posts: 291
Default

Trane XE1000 compressor not coming on line.


Quote:
Originally Posted by Flathead64 View Post
Thank you for all of the help. Iíve learned quite a bit. However, I could not ID the problem so I punted and brought in a service technician. The 59 cent guts of the Schrader valve had failed and nearly all of my R-22 had left to burn a hole in the atmosphere via my wallet.
Thanks again for your time and efforts!
If the low pressure switch locked out the unit due to low refigerant then why did the outdoor fan unit still come on??? It should lock out the contactor from ever being energized??
hennyh is offline   Reply With Quote
Old 11-03-2009, 06:29 PM   #9
Member
 
Join Date: Oct 2009
Location: Nebraska
Posts: 2,362
Default

Trane XE1000 compressor not coming on line.


I don't see a low pressure switch in the diagram. Bet you were right on the first call and the compressor windings opened because it got too hot from the lack of charge.
Marty S. is offline   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
3/4" gas line needs to be bigger raymond_anthony HVAC 11 10-28-2009 05:59 PM
Condensate Line schott HVAC 17 06-02-2008 03:16 PM
high pitch noise coming from oil line pingers7 HVAC 2 11-29-2006 07:41 AM
how to run fridge water line under kitchen floor? travishume Plumbing 23 09-26-2006 07:51 AM
Installing exterior faucet to washer line? skellies Plumbing 3 06-18-2006 08:19 PM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.