Trane XE1000 compressor not coming on line.
I have a Trane XE1000. Believe the compressor is not coming on line. The out door fan is coming on line. What is the best way to determine if power is getting to the compressor?
While I had some one turning the system on and off from the thermostat, I was watching the contactor switch. It was closing and the fan world come on when the switch closed. A few times the switch did not close. Can the switch fail in such a way that the fan receives power but the compressor does not receive power? Thank you,
|
|
|
|
|
|
#2 |
|
Member
Join Date: Nov 2006
Posts: 291
|
Trane XE1000 compressor not coming on line.
You probably need to get the wiring diagram for this specific unit.
In general when the contactor closes it energizes the run winding of both the compressor and fan motor. If the compressor is not comming on then it's internal overload switch could be open or it's run capacitor is faulty. The fan comming on "generally" suggests the contactor is OK. However the starting surge required by the compressor is much larger then the fan motor so I guess the contacts could be marginal. Be careful. Do all your initial diagnostics with low voltage only. Pull the 220v disconnect until you absolutely need the high voltage. |
|
|
|
|
|
#3 |
|
Member
Join Date: Oct 2009
Location: Texas
Posts: 581
|
Trane XE1000 compressor not coming on line.
Is this a heatpump or condenser?
![]()
|
|
|
|
|
|
#4 |
|
Newbie
Join Date: Jun 2009
Posts: 7
|
Trane XE1000 compressor not coming on line.
It is the compressor located in the outdoor unit.
|
|
|
|
|
|
#5 |
|
Member
Join Date: Nov 2006
Posts: 291
|
Trane XE1000 compressor not coming on line.
That schematic clearly shows that the contactor energizes the run winding of both fan motor and compressor. If fan runs and compressor doesn't then I stand by my earlier suggestion to look at run capacitor, compressor overload, wiring or maybe a flakey contactor. (in that order)
Capacitor failures are very common. Does your unit have the start kit?? Sometimes it's only an option for certain applications. Last edited by hennyh; 10-27-2009 at 09:50 AM. |
|
|
|
|
|
#6 |
|
Member
Join Date: Oct 2009
Posts: 67
|
Trane XE1000 compressor not coming on line.
probably the compressor run capacitor is dead
|
|
|
|
|
|
#7 |
|
Newbie
Join Date: Jun 2009
Posts: 7
|
Trane XE1000 compressor not coming on line.
Thank you for all of the help. I’ve learned quite a bit. However, I could not ID the problem so I punted and brought in a service technician. The 59 cent guts of the Schrader valve had failed and nearly all of my R-22 had left to burn a hole in the atmosphere via my wallet.
Thanks again for your time and efforts! |
|
|
|
|
|
#8 | |
|
Member
Join Date: Nov 2006
Posts: 291
|
Trane XE1000 compressor not coming on line.Quote:
|
|
|
|
|
|
|
#9 |
|
Member
Join Date: Oct 2009
Location: Nebraska
Posts: 2,311
|
Trane XE1000 compressor not coming on line.
I don't see a low pressure switch in the diagram. Bet you were right on the first call and the compressor windings opened because it got too hot from the lack of charge.
|
|
|
|
![]() |
| Thread Tools | Search this Thread |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| 3/4" gas line needs to be bigger | raymond_anthony | HVAC | 11 | 10-28-2009 06:59 PM |
| Condensate Line | schott | HVAC | 17 | 06-02-2008 04:16 PM |
| high pitch noise coming from oil line | pingers7 | HVAC | 2 | 11-29-2006 08:41 AM |
| how to run fridge water line under kitchen floor? | travishume | Plumbing | 23 | 09-26-2006 08:51 AM |
| Installing exterior faucet to washer line? | skellies | Plumbing | 3 | 06-18-2006 09:19 PM |