Trane X1000 120/24VAC Transformer - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 01-29-2011, 08:27 PM   #16
Okay - what size fuse would you suggest?
Slim2011 is offline   Reply With Quote
Old 01-30-2011, 01:54 AM   #17
HVAC Supermodel
unicursalhex's Avatar
Rewards Points: 150
Do a continuity check on the stat wire AND the wire going to the outdoor unit, do this before anything else.
unicursalhex is offline   Reply With Quote
Old 01-30-2011, 07:29 AM   #18
Okay I'll check the outside unit today. If there is no short with the outside unit, could it be that when the system calls for heat the heat pump is going to ground? I could put the system in Em. Heat I guess before to see. Any other suggestions are very much welcome and appreciated. Thank you.
Old 01-30-2011, 04:42 PM   #19
I checked the outside unit, no shorts. I'm starting to think maybe the Honeywell control panel might be the culprit. Nothing is making sense as to why something is going to ground. The Honeywell control panel looks normal, no signs of problems.
Old 01-31-2011, 03:01 AM   #20
HVAC Supermodel
Rewards Points: 150
Did you manually jump the unit on? If it runs without the wires and stat and you're sure there are no shorts then go get a thermostat
Old 01-31-2011, 07:27 PM   #21
Thanks guys for all the help you provided. I purchased another transformer and a inline fuse with 3amp fuses. After installing the new transformer with the fuse, I was able to troubleshoot the problem back to the Honeywell Thermostat. It appears 8 years was just to much for it, and it internally gave up the ghost. Problem solved, thank you to all who offer support.
transformer failure in a Trane XE78 turtleescape HVAC 7 07-19-2010 07:34 PM
Unable to find out how to wire a dimmable light transformer Maleko Electrical 9 02-07-2010 01:07 AM
new install of Trane XL15i nind HVAC 32 01-30-2010 12:59 PM
How to install Aprilaire transformer? Studly HVAC 9 09-18-2009 09:44 AM
Comfortmaker RPJ - Bad Transformer? olgranddad HVAC 2 12-26-2008 11:10 AM