My system sometimes just blows ambient air - doesn't cool. I went out and checked and sure enough, the compressor and fan wasn't running outdoors. This is not a heat pump system.
If I go into the basement and turn the switch off next to the air handler, then turn it back on, the compressor and fan start up.
This has been going on ever since I moved into this new house 10 years ago, but usually only happens twice or three times a year.
It has done it 4 times in two days now.
I had to replace the board in the air handler after a lightning strike 1.5 years ago but this changed nothing. At that time there were no leaks and didn't need any refrigerant.
Any ideas?
Thanks.
Brad-Man is offline   Reply With Quote
Old 07-09-2008, 05:56 AM   #2
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
I'd check the obvious first, bad thermostat switch contact, bad t-stat wire, loose connection. I've seen some instances where, when the wire was stripped, it was nicked and the wire broke in a wirenut or terminal and it was just touching enough to make contact, if it moved the slightest, it would open.
wirenut1110 is offline   Reply With Quote
Old 07-09-2008, 03:26 PM   #3
Rewards Points: 150
With a progressive problem my first thought is a weak capacitor . Everything the other guy said is just as likely
geo fan is offline   Reply With Quote
Old 07-09-2008, 06:12 PM   #4
Ouch!That'll leave a mark
Lightbulb
Have you checked the board in the condensing unit? Sounds to me like its locking out on a high or low pressure switch. Is the condensor coil clean? Next time it happens try and locate where you are loosing 24 volts. Trace the wires backwards from the contactor to the compressor protections. By turning the power off to the air handler you are resetting the condensor lock out board.
ridgevilleac is offline   Reply With Quote
New House, new system, poor cooling Faulknertw HVAC 15 07-08-2008 10:06 PM
Is 1/2 Pex more restrictive than 1/2 copper? twilightcall Plumbing 19 06-24-2008 07:32 AM
Radiant Heat System Leak? baeljb HVAC 4 05-21-2008 05:15 PM
boiler / Over-pressurizing cparke HVAC 1 05-21-2008 05:54 AM
Size A/C system properly 70stang HVAC 1 03-26-2006 07:22 PM