Trane Self Igniter Problem - HVAC - DIY Chatroom Home Improvement Forum
Old 05-05-2013, 09:18 PM   #1
I have a Trane XB90 that has stopped igniting. When the thermostat sends a call to run, the fan comes on, followed by the glow bar. Gas apparently does not flow, so glow bar shuts down. After a few seconds, glow bar lights back up but with same results. I've turned the valve off for 5 min and then back on as directed, but with no change. I believe the unit is about 7-8 yrs old, but to me, it looks new inside. Any advice?
pgr380 is offline   Reply With Quote
Old 05-05-2013, 10:18 PM   #2
Rewards Points: 616
you need to find out if the gas valve is getting voltage.....
carmon is offline   Reply With Quote
Old 05-06-2013, 06:38 PM   #3
Rewards Points: 582
yep as carmon said ..need to see if you have 24 volts at gas valve...if you don't most likley bad board...if you do most likely bad valve...ben sr
Old 05-07-2013, 10:08 PM   #4
AKA HVACTECHFW
Rewards Points: 1,208
do you have other gas appliances in the home that are working?
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
The Following User Says Thank You to hvactech126 For This Useful Post:
ben's plumbing (05-07-2013)
Old 05-07-2013, 11:24 PM   #5
yes, downstairs furnace and hot water heaters, all working fine
Old 05-07-2013, 11:53 PM   #6
I'm Your Huckleberry
Rewards Points: 2,270
you need a meter to check across both terminals of the gas valve to see if it's receiving 24 volts.
sequence of operations for a draft induced gas furnace:
1.) inducer (exhaust ) motor starts
2.) pressure switch proves burnt fumes can exhaust by way of pressure switch closing
3.) ignitor lights up
4.) gas valve is sent 24 volts to open, fire starts. there is a distinctive click when the gas valve receives it's 24 volts, after the ignitor is lit up. again, you need to check across the two terminals where the two wires connect at the gas valve for 24 volts. remember, it will only be sent 24 volts once the ignitor is lit up
5.) appr. 30 seconds after burners have lit up and the flame sensor has noticed the flame and they continue to burn, the main blower begins to run.
Thanks.
Doc Holliday is offline   Reply With Quote
The Following User Says Thank You to Doc Holliday For This Useful Post:
ben's plumbing (05-08-2013)
Trane XL1200 - Outdoor Unit Problem snifred81 HVAC 5 08-07-2012 02:53 PM
Trane XE-78 Furnance problem Ona4day HVAC 2 01-20-2012 01:00 AM
new install of Trane XL15i nind HVAC 32 01-30-2010 01:59 PM
Stymied by window leakage problem. Matth3w General DIY Discussions 5 06-11-2008 07:26 PM
Post-Tension Slab Problem Advice/Help Mike McBride Building & Construction 2 01-09-2007 02:51 PM