Trane- Compressor Not Turning On When Calling For AC - HVAC - DIY Chatroom Home Improvement Forum
Old 09-21-2012, 03:28 PM   #1
Trane- compressor not turning on when calling for AC
When the the thermostat in the house calls for cooling the fans turn on but is not blowing cold air. Checked the compressor and it is not turning on. It has power but not turning on. When pressing the middle part of the relay, part# 3100-15Q242, the compressor turns on.
Do I need to replace the relay or am I missing some else that is causing it to not turn on?
Any help would be appreciated.
cpeters is offline   Reply With Quote
Old 09-21-2012, 05:21 PM   #2
JJboy's Avatar
If the Fan Motor is running the "middle part" (Contactor) is pressed and the Compressor should be running. If not, the compressor has open windings or the thermo switch is open.
If you you can make the fan motor and compressor run only by pressing the contactor, you need to test the contactor coil and check for 24vac on the contactor coil.
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
Old 09-21-2012, 09:28 PM   #3
Rewards Points: 582
check for 24 volts at the contactor....
The Following User Says Thank You to ben's plumbing For This Useful Post:
hvactech126 (09-22-2012)
Trane Thermostat Replacement roadbiker255 HVAC 7 07-24-2012 01:29 PM
Trane XR90 - Condensate Drane Trap JDWorks HVAC 16 02-07-2012 07:59 PM
TRANE HVAC breaker turning off crcuevas HVAC 15 01-14-2012 11:26 AM
Ruud vs Trane peter_holmes HVAC 23 07-28-2010 02:32 PM
new install of Trane XL15i nind HVAC 32 01-30-2010 12:59 PM