I installed a new compressor, (2) dryers and (2) check valves, purged system & vacuumed down for (2) hours. Used vacuum in system pull in new R-22 and upon start up to complete charge, compressor starts and stops continuously in 2 second intervals. Voltage checks out, system does the same thing in heating or cooling. Please help???????
Southern Pride is offline   Reply With Quote
Old 01-28-2011, 10:46 PM   #2
AKA HVACTECHFW
Rewards Points: 1,208
did you use a micron gauge to know how good your vacuum was? Most likely you are tripping on high head or low pressure switch. You sure you installed the check valve in the correct direction? Is your contactor opening and closing or is the comressor shutting on and off with voltage still applied?
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 01-29-2011, 07:29 AM   #3
Rewards Points: 1,216
You are probably in the wrong Forum I think this one is more for homeowners your equipment is Industrial/commercial.
You might have to go back to the beginning and ask what was the original problem that caused you to do all that work. And was the original problem the same as the problem now?
COLDIRON is offline   Reply With Quote
Old 01-29-2011, 08:31 AM   #4
An old Tradesmen
Rewards Points: 7,372
Yep, looks like the compressor killing problem is still there.
Of course. it could be that the checks were accidentally installed in the wrong direction.
Old 01-30-2011, 06:23 PM   #5
Question
Thanks for the replies. I am sure the check valves and driers are installed correctly. My thoughts are the compressor in shutting down on high pressure. I do not feel that the high limit switch is faulty because the compressor will start. I am leaning towards a defective reversing valve or maybe a faulty T'Stat. What do you think?
Old 01-30-2011, 07:32 PM   #6
An old Tradesmen
Neither a bad/stuck RV, or a bad thermostat will make a compressor shut down on high pressure.
Old 01-31-2011, 06:37 AM   #7
Hey Southern you said your thoughts are it's shutting down on high pressure.
That should have been eliminated right away that is one of the easiest things to check. So here's what I would do before you spend any more time and money, call a commercial pro to help you with this equipment. Or install tattletales on the safety circuit.
Old 01-31-2011, 06:56 AM   #8
Deleted
Old 02-01-2011, 04:17 PM   #9
Thank you for your input, now for the results:
The system was shutting down on low pressure because the vacuum was now was not enough for initial start up. After force feeding the system and weighing in 26 lbs of R-22 system ran fine after freeing up a stuck RV. Completing the task by charging using a sub cooling calculator unit is running great. Special thanks to Beenthere & ColdIron.
How to stop auxillary heat from coming on defrost cycle and limit auxillary heat use? twilightcall HVAC 34 12-28-2010 06:53 PM
heat pump question David from MD HVAC 3 02-01-2010 08:42 PM
trane x19i heat pump MrSnapRon HVAC 8 08-29-2009 01:17 PM
Heat Pump vs Aux Electric Heat batolson HVAC 16 01-17-2009 10:28 AM
Trane Heat Pump tstat replacement with Honeywell prog - wiring question sep23 HVAC 2 10-20-2006 09:10 PM