Thermostatic duct adjustment
I have a server cooling dilemma. The 3 ton rooftop HVAC that cools the server room also cools 2 other rooms. The server room needs more or less cooling depending on load and season. The 2 other rooms end up freezing when the servers are working hard but are fine when the servers are at idle. If the vents are shut to the non-server rooms they get too hot.
Question: Is there a thermostatically controlled vent or duct that can pinch off flow to the non-server rooms when they reach a comfortable temp? I figured 2 adjustable vents and 2 more thermostats to adjust them. Please understand, I realize balancing these systems is an art and that what I'm suggesting is using a sledge hammer to fix it.
carbunkle is offline   Reply With Quote
Old 04-12-2010, 12:25 PM   #2
An old Tradesmen
Rewards Points: 7,318
You can installing a zoning panel and dampers to do what you want(along with a barometric bypass damper).
The Following User Says Thank You to beenthere For This Useful Post:
carbunkle (04-12-2010)
Old 04-12-2010, 12:55 PM   #3
biggles's Avatar
they have motorized registers that would replace the exsisting on the non-server room 24V and stat and your controlling the space.the dampers are not air dependent and basically would be moving/modulating even if the unit is off..then close when the statis satisfied....will hunt them and get back....
The Following User Says Thank You to biggles For This Useful Post:
Old 04-12-2010, 01:07 PM   #4
biggles's Avatar
options are to replace the register or cut into the duct as shown ...home theater is typical off the main unit as shown to control the area. http://www.cinemabuilder.com/products/HVAC/hvac.asp
Old 04-12-2010, 01:13 PM   #5
Thumbs up
After posting, of course, I searched using the right terminology "damper". This, as you know, got the hits I was looking for. The Honeywell system seems to be well sorted out (and a little pricey). Thanks for all your replies. Glad to be part of a forum with active members.
Old 04-12-2010, 01:21 PM   #6
Hvac Pro
yuri's Avatar
Rewards Points: 2,240
Make sure you get a reputable professional to do your work. The drawbacks are that when the non server dampers close the velocity and noise of the air in the server room will increase. This can also overload the fan and cause potential freezeup of the A/C coil and overheat the furnace part if it has one. You need to make sure or the Pro does that there are no freezeup problems when reducing the airflow and even barometric damper setups are not perfect. The ideal setup is separate units for the 2 different areas. Minisplit units are popular for server rooms:Fujitsu Ductless Mini-Splits: Wall Mounted Systems
Old 04-12-2010, 06:05 PM   #7
An old Tradesmen
Only problem with that method. Is that if both of the non server rooms have their dampers closed. Then the air flow will be too low. Probably freeze up the evap coil. End up with the server room over heating. And flood back the compressor and probably damage it.
Zoning systems. While more expensive. Have safeties to protect the HVAC equipment.
Old 04-13-2010, 10:18 AM   #8
The server room has 2-12" ducts going from the main distribution manifold, or whatever it's called, to the room. The HVAC is shooting to 2 rooms. I only need to close one of the 3 - 12" ducts. There are no restrictors or dampers on the server rooms registers, just diffusers. The reason I'm in the DIY section is because we can't afford a pro right now. We have to squeak by on our wits. We are pro's at what we do and hate when people try to do our jobs too, so I understand but we have no choice right now. I'll take all of your warnings seriously. Thank you very much for your time.
Old 04-13-2010, 02:14 PM   #9
An old Tradesmen
I'm not telling you this needs to be done ny a pro.
I'm telling you how to do it right so that you don't end up with a dead compressor. And servers that shut them selves off. And end up closing down your operation.
Do you know how many tons your A/C is.
Old 04-13-2010, 02:29 PM   #10
Carbunkle?
http://www.google.com/search?client=...UTF-8&oe=UTF-8
Duct work in garage. flashme18 HVAC 1 11-08-2009 06:29 PM
Return duct "boot or no boot" ads67 HVAC 16 01-10-2009 09:38 AM
Furnace install in attic - Duct configuration hartkem HVAC 6 11-08-2008 05:46 PM
Flex Duct Advice ssporty21228 HVAC 4 07-23-2008 08:28 PM
Condensation in Wall: Can I Seal a Dryer Duct With Caulk? xquercus HVAC 5 07-01-2007 02:33 PM