-   -   Thermostat wiring question (http://www.diychatroom.com/f17/thermostat-wiring-question-59211/)
cpuken 12-13-2009 09:11 PM
I have a carrier heat pump with a honeywell thermostat. I just purchased a digital, programable thermostat and needed assistance on how to wire the new thermostat.
Current Honeywell thermostat wiring is as follows:
Terminal Wire_Color
G Green
C Blue
R Red
W1-Y Yellow (W1 & Y terminals are jumpered)
W2-E White (W2 & E terminals are jumpered)
B Black
O Orange
New TS21 thermostat
Terminals
I2
I1
RC
DH
H
C
Y2
RH
OBW
W2
G
Y1
here's a link to the TS21 manual:
http://www.diversitech.com/literatur...hermostats.pdf
Help please
Ken
Houston204 12-13-2009 10:22 PM
Post the model number of your old stat.
If the subbase has a Q674?-???? number, post that as well.
Is this controlling a zone system? It is unusual for both O and B to be in use unless B is actually E or C , and this is not your case.
cpuken 12-14-2009 05:58 AM
The old thermostat model number is T8411R (Honeywell).
Here's a link to the manual for it.
http://customer.honeywell.com/Techli...0s/69-1037.pdf
Ken
cpuken 12-14-2009 07:25 PM
No, this is not controlling a zone system.
See my other response for more details on the existing Honeywell thermostat.
beenthere 12-14-2009 07:32 PM
RH (jumpered to RC-red
C-blue
Y1-yellow(DO NOT JUMPER TO W)
W2-white
OB/W-orange
G-green
Check your air handler. You should not need the wire that was attached to B on your old thermostat.