Thermostat For Electric Baseboard Heat 4 Wire To 2 Wire - HVAC - DIY Chatroom Home Improvement Forum
Old 01-03-2009, 05:02 PM   #1
Thermostat for electric baseboard heat 4 wire to 2 wire
I am replacing my old Honeywell CT60B with a new programable Honeywell.
The old stat has two black and 2 red wires, the new one has 2 black. I think I should connect the 2 reds together and the 2 blacks will be wired to the stat.
Is this correct? How can i test to make sure I'm doing it correct. (FYI I have a volt meter)
rossl56 is offline   Reply With Quote
Old 01-04-2009, 07:41 AM   #2
An old Tradesmen
Rewards Points: 7,372
I thought code reuired the stat to open both legs on line voltage heat controls.
Personally, I won't install a 2 wire line voltage stat.
Old 01-04-2009, 12:50 PM   #3
Rewards Points: 1,514
Assuming your city's code allows single pole (2 wire) electric heat thermostats, start with all four wires disconnected. Only one pair combination will register voltage (usually 240 volts) when you test using your voltmeter. To double check, the pair that registered voltage should come from the same cable entering the back of the wall box.
Turn off the power again.
Tie together one wire from the pair that registered voltage and one of the other wires. Connect the other wire from the pair that registered voltage together with the other remaining wire to the thermostat.
OT: As far as double pole thermostats go, it is not unusual for one of the poles to make/break at a different temperature from the other. Your own calibration may be needed. This sometimes requires scraping glue or paint from the adjusting screws and putting fresh (or nail polish) back when you are done to hold the calibration.
Old 01-04-2009, 01:10 PM   #4
Hvac Pro
yuri's Avatar
Rewards Points: 2,276
""OT: As far as double pole thermostats go, it is not unusual for one of the poles to make/break at a different temperature from the other.""
How would you know this is happening??
Old 01-04-2009, 01:34 PM   #5
An old Tradesmen
Its a safety feature.
Minimizes the chance of both contacts fussing together.
Old 01-04-2009, 03:02 PM   #6
Should I get a double pole? If it is "safer" I would prefer it. What are the benefits?
Old 01-04-2009, 04:04 PM   #7
Hvac Pro
yuri's Avatar
It is safer and meets the electrical code. Replace the one you have with the same kind. If not and there is a fire the fire inspector and insurance company will nail you.
Old 01-04-2009, 06:25 PM   #8
An old Tradesmen
When set to off.
Now electric is at the heater.
Only one pole arcs when it turns the heater on or off.
Old 01-04-2009, 06:33 PM   #9
Electrical Contractor
kbsparky's Avatar
Double pole line voltage thermostats have an "off" position. When set to "off" the thermostat acts as a disconnecting means, and all power to the unit is disconnected.
Single-pole thermostats have a "low" position, but no "off" -- there can be voltage present at the heating unit no matter where the thermostat is set. You always have a minimum setting on these, and the heat will come on at some point during low ambient temperature conditions.
Old 01-05-2009, 12:18 PM   #10
I installed it last night without a problem. I went back to Lowe's and HD to purchase a 4 wire unit, but they don't carry the programable 4 wire stats
Honeywell sells this for "Contractor Installation" only. I guess due to the 240volt/3K watts issues, I assume you could fry the unit if you hook up the wires wrong.
Today, I did order the Honeywell TL8230a since this is a double pole type (4 wire). It seems like the safer way to go. Found it at a good price at PEX
http://www.pexsupply.com/index.asp
Thank you to all that responded, I probably would have "settled" for the 2 wire if I didn't hear such strong responses about it.
Old 01-05-2009, 10:05 PM   #11
An old Tradesmen
Your welcome.
And much much better off now.
Old 11-12-2014, 04:05 PM   #12
Help please
I'm confused on the wiring from my old stat to new stat. New stat is Honeywell rlv4305 with 2 wires. Old stat has four wires. I no 2 legs are 120 volt feeds and pretty sure other 2 wires are from baseboard heater. Not sure what wires to connect to stat and together. Any info. Would be greatly appreciated as I just spent a lot of money on 5 of these for 5 seperate rooms.
Emm1212 is offline   Reply With Quote
Old 11-12-2014, 04:10 PM   #13
An old Tradesmen
Wire 1 line wire to the stat, and 1 load wire to the stat. Wire nut the other 2 wires together.
The Following User Says Thank You to beenthere For This Useful Post:
Emm1212 (11-12-2014)
Finned-tube elements for hot water baseboard heat SureBert HVAC 2 12-05-2008 05:01 PM
8 wire to 4 wire thermostat help needed dj petey Electrical 5 01-19-2008 09:11 AM
2 stage heat thermostat problem W1 AND w2 wires whatdoIdonow HVAC 6 11-26-2006 12:04 AM
8 wire to 4 wire thermostat help needed dj petey HVAC 5 04-15-2006 12:20 PM