Tempstar Problems - HVAC - DIY Chatroom Home Improvement Forum
Old 11-06-2011, 01:11 PM   #1
tempstar problems
I have a tempstar PA5542AK with heat strip AMMK17AHb2 that I can not get the heat srips to come in.
I get 24 volts to the sequencers and 110volts from them to the strips and through the limiters.
I checked the continuty of the strips which are good.
I checked the continuty of both sequencers with 24 volts to the coil which checked out.
I disconnected all wires from both sequencers and checked the ohms. the 2 stack was 58 ohms and the three stack was 78.
Funny thing is I can start a heat cycle with the fan unplugged and the strips will power up and run fine if i plug the fan back up before the limiters trip.
scottie9656 is offline   Reply With Quote
Old 11-06-2011, 01:39 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 1,862
You should have 220-240 volts coming into the unit ACROSS both wires and do not test each to ground. Lots of guys get fooled when they get 110 to ground which is NOT a real 220. Same thing when testing the elements. Need to have 220 across them and not test to ground. Same thing happens when testing AC contactors. If you only have 110 then one of your main fuses is blown or breaker tripped. You should draw around 18-20 amps on a 5kw element with 220/240. Will still work with 110 but produce half the heat. Lectric furnaces can be tricky to troubleshoot.
Old 11-06-2011, 02:20 PM   #3
I do have 220 volts at the elements pulling 20 amps when I get them to come on.
Old 11-06-2011, 04:01 PM   #4
Hvac Pro
yuri's Avatar
If it has a small circuit board or relay interlocked with the sequencers to turn the fan on with the AC that may be acting up and causing a problem.
Old 11-06-2011, 04:41 PM   #5
Is there any way to test the circuit board? How about the test on the sequencers? I read I should not be getting more than 20 ohms thru the coils on the sequencers.
Old 11-06-2011, 05:13 PM   #6
Hvac Pro
yuri's Avatar
Sounds like you are getting some sort of backfeed and more than 1 motor winding or circuit in the 24 volt loop energized . A sequencer does not need to be tested that way. It either closes or opens. Nothing more than a warp switch. Post a pic of the electrical diagram and maybe we can read it and help more.
Old 11-07-2011, 07:54 AM   #7
tempstar problems
Here we go.
Problems with Square D Subpanel bltglt507 Electrical 16 12-04-2009 08:44 PM
Multiple problems in 3 year old house I just purchased swenard Plumbing 12 08-31-2009 03:53 PM
How to diagnose problems with wall kahlan General DIY Discussions 5 10-22-2008 09:18 AM
Elec short causing A/C problems or A/C problems causing elec problems? Marlon Electrical 2 06-25-2008 02:04 PM
Are you having ice problems? Grumpy Roofing/Siding 27 02-17-2008 03:51 PM