Tempstar Circa 1990-ish - HVAC - DIY Chatroom Home Improvement Forum
Old 01-20-2009, 08:18 PM   #1
Tempstar circa 1990-ish
I was hoping to get a little help from the masters of HVAC. I'm having trouble diagnosing a tempstar furnace. The blower runs all the time. Even without the t-stat being wired to it. It has intermittent spark ignition. I changed the board, but that didnt do anything. Would it be the limit switch? and if so can I jump it, to see if that is the problem. The wiring diagram shows a normally closed limit switch. Any help would be awesome.
Rookietinner is offline   Reply With Quote
Old 01-20-2009, 09:14 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 2,286
ICP and Carrier will run the fan continuously if the limit is open (to cool off the hot heat exchanger is the rational). You can test it with an ohmeter. I will never recommend jumping them as some fool may leave a jumper on for "temporary" heat and kill someone.
Old 01-20-2009, 10:23 PM   #3
Dr Heat's Avatar
if it were an open limit the furnace would not fire check the board ICP has a constant fan stake on be sure you wired to heat and cool
Dr Heat is offline   Reply With Quote
Carrier Cobra circa 1996 w/ electronic ignition ChuckT HVAC 4 11-03-2011 06:36 PM
Problems with Carrier Furnace circa 1990 Blue2 HVAC 4 11-27-2008 06:32 PM
Tempstar issue with cooling cycle Teddy1731 HVAC 2 07-08-2008 10:15 AM
1990 Celica Back-Up Light Switch slickshift Automotive Repairs 4 06-10-2008 07:36 PM