Temperature Rise - HVAC - DIY Chatroom Home Improvement Forum
Old 03-15-2009, 04:52 PM   #1
Temperature Rise
Goodman 5 Ton Heat Pump with Variable Speed Airhandler
Outdoor Temp = 46
Supply Air Temp = 103
Return Air Temp = 70
Temperature Rise = 33
Is this temperature rise to high or ok in relation to CFM setting? The temperatures were taken with the heat strips off and thermostat set to 72. The airhandler is currently set at 1530 CFM.
mjbxx is offline   Reply With Quote
Old 03-15-2009, 04:59 PM   #2
An old Tradesmen
Rewards Points: 6,092
Too high period.
Indicates too low of an air flow for the unit.
Old 03-15-2009, 05:15 PM   #3
Got it. Should I just increase the CFM setting to correct? And what should the temperature rise be?
Old 03-15-2009, 05:21 PM   #4
GC/Master Plumber/Mech
Rewards Points: 560
You may have a setting of 1680 but is this your actual CFM
To calculate CFM follow this
CFM = (Volts X Amps X 3.413) divided by ( Temp rise X 1.08)
Your system may be under charged. I would have it checked. Keep in mind the only true ways to check a charge in a heat pump are
1. Checking super heat and sum cooling in a/c mode on a warm/hot day
2. Weighing the freon in on a cold day.
It is best to check charge in the summer just before going into winter.
Also your second stage heat can be set up for stages to come on in the fall/winter. As the tempout side drop the effenicy of the heat pump drops as well.
On the days where it is cold it is not as simple as adjusting blower speed to get more heat. There are other factors as duct work as well.
Is this a new install, replacement or an appliance that you have had for a while.
What made you check temp rise?
Old 03-15-2009, 05:24 PM   #5
An old Tradesmen
You shouldn't be 33 until 55 or better outside.
You should have 1850 or better CFM.
Goodman generally want 400 CFM per ton in heating mode.
Old 03-15-2009, 05:33 PM   #6
If what you are saying is true, then why does Goodman allow for a 15% reduction of the trim adjust setting which lowers CFM to 1530 from 1800?
Last edited by mjbxx; 03-15-2009 at 11:36 PM. Reason: Reduction should be 15% lowering CFM to 1530
Old 03-15-2009, 05:56 PM   #7
An old Tradesmen
For comfort.
It lowers the efficiency, but gets you a warmer discharge temp.
They, like most manufacturers, don't tell you that part.
They also don't tell you that it increases the amount of time it takes to defrost the coil.
Old 03-15-2009, 11:05 PM   #8
OK. Should I just place the system back to 1800 CFM? I have to say that since I lowered the CFM on the system, the house has been much more comfortable and in fact, the system does not seem to run as long as the previous setting. I suppose if our next electric bill rises, I'll know it is not as efficient.
Old 03-15-2009, 11:21 PM   #9
An old Tradesmen
Set it to where it makes you comfortable.
Old 03-15-2009, 11:40 PM   #10
Originally Posted by beenthere View Post
For comfort.
I didn't know that
hvaclover is offline   Reply With Quote
Old 03-16-2009, 05:25 AM   #11
An old Tradesmen
Your actually removing less heat from the discharge gas.
With the lower indoor air flow, it doesn't supply as much heat to the outdoor coil to thaw it.
Condensation on fiberglass window frame creamaster General DIY Discussions 11 01-05-2012 08:42 PM
how to stop condensation on windows? cake General DIY Discussions 7 11-22-2008 01:12 AM
Sweating windows big daddy-o General DIY Discussions 15 01-06-2008 03:41 PM
Temperature Differance Over Coil rjordan392 HVAC 9 08-11-2007 06:34 PM