jim360 02-11-2010 08:04 PM

temp. control problem
 
furnace seems to drop in temp. when I reset temp. rises back to setting
I have a concord furnace, it is about 6 years old

beenthere 02-13-2010 07:47 AM

Does that mean your stat calls for heat but the furnace doesn't come on. Until you turn the stat down and then back up?

jim360 02-13-2010 09:42 AM

temp. control problem
 
yes, but it takes some time for the pilot to light

NHMaster 02-13-2010 10:19 AM

The anticipator in the thermostat may be set to the wrong milliamp setting. Is it pilot ignition or Hot surface?

jim360 02-13-2010 01:17 PM

I believe it is hot surface

jim360 02-13-2010 02:15 PM

temp. control problem
 
do you think it could be the hot surface ignitor, if so which one do you recommend. the carbide or nitride

beenthere 02-13-2010 03:15 PM

Its probably not the HSI.
What brand and model is the thermostat, and furnace.

jim360 02-14-2010 07:56 PM

temp.
 
the stat. is a honywell and the furnace is a concord(2004)90% eff.
getting fault that reads: lock-out due to no ignition-7 flashes

beenthere 02-14-2010 08:06 PM

Honeywell makes more then 500 different thermostats. So what model number is yours.

Could be a pressure switch, or flame sensor.

Now if its a model, for get it. Your concord probably isn't that model.

jim360 02-14-2010 08:24 PM

temp.
 
honeywell-CT3451
concord-8404G08507

beenthere 02-14-2010 08:32 PM

Check your flue/chimney for restrictions.
check hose to pressure switch for moisture in it.