Superheat Vs Subcooling Method For Adding R22 - HVAC - DIY Chatroom Home Improvement Forum
Old 07-08-2011, 02:55 PM   #1
JJboy's Avatar
1- run the condenser for 15 minutes
2- Read the liquid pressure at liquid line port at the condenser
3- Read temp at liquid line near the liquid line port.
4- Subtract the measured liquid line temp with saturation temperature ( R22 Pressure chart )
Ex:
Liquid Line Pressure: 200PSIG
Saturation temp ( pressure chart ) : 100F
Liquid Line temp (probe): 90F
Subcooling = 100F - 90F = 10F
This is your real subcooling. You need to know target subcooling also
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
TXV and superheat DIY_HVAC HVAC 39 12-31-2011 07:23 AM
Need help choosing the easiest method for skim coating fortunecookies Drywall & Plaster 2 03-05-2011 03:09 PM
SuperHeat & Subcooling JJboy HVAC 7 03-04-2011 07:00 PM
Goodman heatpump subcooling too high Rollie HVAC 4 01-06-2011 11:27 AM
superheat -1 wetbar HVAC 30 07-21-2010 05:49 PM