Split System Line Set Sizing - HVAC - DIY Chatroom Home Improvement Forum
Old 04-14-2011, 07:50 AM   #1
I am installing two split systems. One is 1.5T the other is 2T. Each is using an ADP Series R air handler and a Ducane condenser. The Air handlers are located in the attic, and the condensers outside. The elevation difference between the air handlers and the condensers is 11'. The 1.5T will be approximately 60' no greater than 75'. The 2T system will be approximately 50' no greater than 60'.
So if I understand correctly I have < 75' linear feet, and 11' liquid lift.
I intend on running 3/4" Suction lines and 3/8" Liquid Lines. Do these seem appropriately sized?
yogi_bear_79 is offline   Reply With Quote
Old 04-14-2011, 09:51 AM   #2
30 year tech
hvac122's Avatar
You need to follow the manufactures charts for that specific match.
hvac122 is offline   Reply With Quote
Old 04-14-2011, 10:29 AM   #3
I have read the charts, but not being an expert I was hoping for some guidence that I was reading them correctly.
From what I can tell My Liguid Line can be 5/16" on both units (Lineset1.jpg)
(LineSet2.JPG) has the chart for the vapor line, here it looks like 5/8" is acceptable.
Unfortunately my salesmen is not helpful on this matter. I am fine upsizing to 3/8 & 3/4 if that is required. I am using HFC-410A refrigerant.
Split System Line Set Sizing-lineset1.jpg   Split System Line Set Sizing-lineset2.jpg
Old 04-14-2011, 05:31 PM   #4
An old Tradesmen
Rewards Points: 6,906
3/8 x 3/4.
The Following User Says Thank You to beenthere For This Useful Post:
yogi_bear_79 (04-18-2011)
Old 04-14-2011, 05:59 PM   #5
Hvac Pro
yuri's Avatar
Rewards Points: 1,842
Not sure if you plan to use a TX Valve, thermostatic expansion valve but if the systems are for yourself I would. Gives you far better control of evaporator coil temp etc. May help if there are any issues once you get to the 50 foot length of line. Not all coils easily accept them so you need to find out ahead of time if yours does. You should also install a secondary drain pan to protect the ceiling from damage and I would recommend a water bug detector to set off an audible alarm if water gets in there or one of these. These can be wired in to shut off the condensor.
http://www.diversitech.com/prod/wet_switch.php
The Following User Says Thank You to yuri For This Useful Post:
Old 04-18-2011, 08:18 AM   #6
We have installed the drain pans, with alarms. Went with the 3/8 3/4 lines, and have plans for the TX valves.
Need help sizing duct trunk addition to system. chryste HVAC 6 10-03-2010 01:59 AM
installing a split system Jacques HVAC 6 07-10-2008 08:50 AM
New House, new system, poor cooling Faulknertw HVAC 15 07-08-2008 10:06 PM
Is 1/2 Pex more restrictive than 1/2 copper? twilightcall Plumbing 19 06-24-2008 07:32 AM
boiler / Over-pressurizing cparke HVAC 1 05-21-2008 05:54 AM