-   -   Soft lockout in Burnham Alpine 150 (http://www.diychatroom.com/f17/soft-lockout-burnham-alpine-150-a-167346/)
Billm10454 12-25-2012 02:02 PM
The lcd display on my furnace alternates between b 26(soft lockout) and 9 116 then 115 and so on until it reaches 110. The heat does come on and heats the house. I have 2 zones of baseboard. I had the main circulator pump replaced 2 weeks ago. I called Burnham but they are no help at all. Anyone have an idea what it is. This happens all day long but the heat does come on.
beenthere 12-25-2012 06:37 PM
B26, boiler safety limit, or external limit wired to terminals 3 and 4 is open.
Check for these possibilities.
• Heating load at time of error was far below the minimum firing rate of the
boiler
• Defective primary pump or no flow in primary loop (Piping Method 1)
• Control system miswired so that boiler operation is permitted when no zones
are calling
that is from the install manual.
Billm10454 12-26-2012 10:48 AM
Primary pump was replaced 2 weeks ago and the system was bled.
Not being a plumber I don't know what about the first possibility
Control system must be wired correctly because the was installed 2 years ago.
Today it has been running correctly
Billm10454 12-27-2012 11:26 AM
The manual says that the 9 in the lcd screen means it is possibly a bad DHW sensor. Should I just change it even though I get heat and hot water?
beenthere 12-27-2012 04:54 PM
Can't tell you from here. may want to get one just incase.
Billm10454 01-01-2013 01:04 PM
The problem was the high limit switch. Replaces it now everything is running OK