Old 12-21-2010, 09:15 PM   #1
SO SO Lost??? Changed Board and Motor and still nothing
Okay...
So I changed my mainboard and motor as per my service guy said on his ticket when he came out
I changed the board
and connected everything back to where it belongs
(because I labled every wire)
then took out the blower motor
and got a new one
Same spec plus a new capacitor
Now... here is the kicker...
Cooling is working, Furnace lights up and is burning...
but no blower running
the motor is just not running
is there a way I can jump some thing to make it run
I have a 4 speed
Please Help
As I am about to go away for the Holidays and dont want my pipes to freeze
kuteazn1 is offline   Reply With Quote
Old 12-21-2010, 09:33 PM   #2
Professional
what are your blower wires connected to on the board? also does the fan run continuous if you move fan to on position on stat?
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 12-21-2010, 09:38 PM   #3
okay
here is what I got
yellow = M2
red = fan
blue = heat
black = cool
white = neutrals
brn/w = cap
brn = cap
NO FAN... Motor will not run
this a brand new board and unit
Old 12-21-2010, 09:43 PM   #4
Professional
Originally Posted by kuteazn1 View Post
okay
here is what I got
yellow = M2
red = fan
blue = heat
black = cool
white = neutrals
brn/w = cap
brn = cap
remove black wire from board connected to x-fmr. put black wire from cool on this terminal. push in door switch. if it runs then no signal from board to motor. if not then bad motor.
IT IS WHAT IT IS
Old 12-21-2010, 09:49 PM   #5
did this to the last board too
by past it to get the motor running
(the HVAC Tech did this still have his jumper)
got new board and new motor
now same problem
I did the black to XFMR and still nothing
can it be the thmostat?
Old 12-21-2010, 09:53 PM   #6
Professional
no. if that did not work then you need a meter to check voltage from board. if your not getting anything from the motor when you put the fan to on on stat or in cooling or heating, then it is most likely the motor. check for 120v between fan (red) and neutral (white) when fan is on at stat and system is off @ stat
IT IS WHAT IT IS
Old 12-21-2010, 09:54 PM   #7
i think i am gonna have to bite the bullet and call a HVAC guy to come out and fix it...
Old 12-21-2010, 10:09 PM   #8
if I dont get 120V
what could be the problem
Old 12-21-2010, 10:11 PM   #9
Professional
board. ck for 24v between g and c
IT IS WHAT IT IS
Old 12-21-2010, 10:17 PM   #10
i just bought this board
so right now I dont have a meter reader
so I am heading to Wally World to get one...
will be back in 45 mins
and let you know what I find out
Old 12-21-2010, 11:36 PM   #11
okay so CY I get nothing CR I get 24
the Red/Black/Yellow/Blue into White
I get 127 V
so is the CY the deal breaker?
Old 12-22-2010, 03:05 AM   #12
hvaclover's Avatar
Why do you have red going to fan? That is supposed to be on a park terminal when not used.
Your heat wire should be the blue one only.
If you are measuring voltage off all your motor wires than that is not normal.
Hookup the blue and the white motor wires to a voltage source. I f the motor does not turn over it might be ruined. The fan terminal has a different function and sounds like it caused you motor to back feed thru all you motor windings. That will burn them out if not remediated quickly enough.
Just slow, not stupid.
hvaclover is offline   Reply With Quote
