Old 05-28-2010, 11:06 AM   #1
Slowing down Trane XV95 blower
Hello,
I've got an oversized 5-Ton Trane XV95/XLi20 in a zoned system that I'd rather slow down than scrap.
It's currently set at 350 CFM and showing poor moisture removal.
My zone control will shut down if the DATS goes below a set temperature, so I'm not too concerned about over-cooling and subsequent equipment damage.
How do I take this unit to a slower speed?
Thanks,
DK
DukeKilroy is offline   Reply With Quote
Old 05-29-2010, 12:20 AM   #2
Houston204's Avatar
You might also check for return air leaks and have the refrigerant charge checked...
Houston204 is offline   Reply With Quote
Old 05-30-2010, 04:11 PM   #3
Thanks Houston. Are you saying that to go from 1780 to 1670 cfm (@ 0.5 SP), just change jumpers from:
OFF OFF OFF ON
to
ON OFF OFF OFF
is it that simple?
Duke
Old 05-30-2010, 05:10 PM   #4
Houston204's Avatar
Remove power and give it a minute before changing your settings.
It must not be That simple, I've seen quite a few that were never changed from the factory setting to the correct setting for the application.
The condensation was actually blowing off of the evaporator coil, and missing the primary pan, the last time I saw this.
Old 05-30-2010, 08:26 PM   #5
From the chart looks like 350 is as slow as it goes. Now what does he do? Smaller unit if Freon level is ok?
bob22 is offline   Reply With Quote
Old 05-30-2010, 11:18 PM   #6
Houston204's Avatar
This furnace can be configured for 4 ton 450, 400, and 350 cfm per ton as well.
Bryant Plus 90 - No Blower Ducaticorse HVAC 11 10-16-2012 09:39 PM
Trane XL80 blower motor part number? keverino HVAC 17 01-10-2012 10:01 AM
Trane Furnace Blower Running Nearly Continuously stephensandlin HVAC 3 01-03-2010 02:21 AM
Trane XV 90 shuts off burner and exaust blower zootjeff HVAC 0 12-02-2009 12:50 AM
Trane xv80 furnace blower not working jim2138 HVAC 2 03-22-2008 05:55 PM