Size A/C system properly


I have had my house looked at by 4 contractors and have received two "Manual J" reports.

The house is in CT. 2071 Sq. ft. single story ranch. Base board hotwater heat, and typical split system A/C in attic.

Current 3 ton system installed in 1971 when house was 1350 sq.ft. House was added to in 1996 and since then the current system cannot keep house cool (below 80) on hot summer days. I have to system turned low so its cold at night (66) to keep it livable during day.

R13 in walls
R38 in Attic
Anderson Low E glass windows installed in 1996.
Full Cellar with R19 in Floor

Contractor #1 in 15 minutes told me I needed a 4 ton unit.
Contractor #2 took 2 days send me a quote and recommended a 3.5 ton unit.
Contractor #3 took 2 weeks said he did a complete Manual J load calc. and recommended a 3 ton system.
Contractor #4 took a month mailed me a quote and his "Wrightsoft" Manual J load calc. report showing a result of 2.3 tons which he recommends installing a 2.5ton system.

Appears I have a large difference in size system.
Anyone have any advice?

Thanks

70stang is offline   Reply With Quote
Old 03-26-2006, 07:22 PM   #2
sub-contractor
 
Join Date: Feb 2006
Posts: 49
Default

Size A/C system properly


mustang,

something doesn't sound right with your estimated R-value.

hot in the day and cold in the night? with an R-value like your describing, this should not be the case.

Typical installation here in chicago for your home would be 3.5 ton. Your contractors need to take a good look at the sheetmetal to ensure that it is sized properly, and that the furnace is sized properly as well.

It sounds to me that you have built an addition without spending the money on properly changing the furnace and sheetmetal to accomodate your new load. even with a new properly sized A/C, you will still experience these problems until the whole system is properly sized to accomodate.

simply just tapping new runs off of the sheetmetal that was designed for the 1300 sq ft home will leave you with the exact problem that you are describing. an addition like that would have led you to replace the whole system, or add a new system with it's own unit for the new addition.

Ace


Last edited by Aceinstaller; 03-26-2006 at 07:26 PM.
Aceinstaller is offline   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Size of whole house fan needed Doug Crf General DIY Discussions 20 02-25-2011 11:29 PM
Water Purification System - Maintenance Qs cjcocn Plumbing 1 11-18-2008 07:31 AM
Zone system not working with heat. deliriousga HVAC 5 12-29-2006 06:04 PM
Replace furnace, coil and duct system sps123 HVAC 2 01-07-2006 10:56 AM




Top of Page | View New Posts

Copyright © 2003-2014 Escalate Media. All Rights Reserved.