Should I Connect My W2 Control Board Terminal To Aux Or E On The Thermostat? - HVAC - DIY Chatroom Home Improvement Forum
Old 01-04-2016, 08:07 PM   #1
Rewards Points: 138
Should i connect my w2 control board terminal to aux or E on the thermostat?
also, where should i connect the W/E control board terminal on my thermostat? is it the E terminal? note, the white wire that comes from the outside condenser connects to the W on the board.
i am using a th7220u1035 honeywell and a e2eh-012ha furnace. below are some pictures:
https://goo.gl/photos/dvnLEqGa1ovdFBFE7
https://goo.gl/photos/7X32xnvFHmPNxYkE9
form8829 is offline   Reply With Quote
Old 01-04-2016, 08:21 PM   #2
Rewards Points: 7,906
do you have a dual fuel system?
My Backround FIY: I am not in the business of any trade or topic I give advise on. I have some have formal education in HVAC + some DIY experience. Theory is not a substitute for experience.
user_12345a is offline   Reply With Quote
Old 01-04-2016, 08:28 PM   #3
Rewards Points: 138
user_12345a, i have a 2 heat and 1 cool heat pump system.
Old 01-04-2016, 09:10 PM   #4
Model number shows an electric furnace/air handler.
Not familiar with it, but odds are the electric backup is staged by the board.
Most heatpump style thermostats don't allow for staging the heat strips. Some of the better ones will.
What problem are you trying to solve?
Normally only the heatpump should come on, if you turn up the heat the backup will come on. W1 will turn on the first stage and the second stage may be timed. there may be a jumper between w1 and w2.
Old 01-05-2016, 04:31 AM   #5
An old Tradesmen
Rewards Points: 7,764
Jumper E to Aux on the thermostat, then connect the white wire from the air handlers W terminal to either the aux or E terminal.
Old 01-05-2016, 10:07 AM   #6
Rewards Points: 138
thank you user_12345a.
Old 01-05-2016, 10:08 AM   #7
Rewards Points: 138
thanks beenthere.
Old 01-05-2016, 10:12 AM   #8
Rewards Points: 138
by the way, how does the w2, aux & E work? is w2 the 1st stage heat and aux/e the 2nd stage heat (heat strip)? in this scenario, why put up a jumper between E & Aux?
Old 01-05-2016, 11:58 AM   #9
First stage heat is the heatpump, applies voltage to Y, G.
If the heatpump can't keep up without help, the stat applies voltage to W1 as well, brings on the electric heat.
E is separate and energized when you set the t-stat to emergency heat to shut down the heatpump. The terminal is there for when emergency heat entails doing something different from just switching on the electric heat; for example, manually switching over to a fossil fuel furnace when there's electric backup as well.
With a straight electric system, no fancy stuff -> E is jumped to W1/aux to bring on the electric heat.
W2 is second stage aux heat; if you wanted to keep part of the heat strips off until it gets really cold (as to save energy during defrost cycles, not get short blasts of hot air), you could get a thermostat that can stage the backup heat. From the factory these air handlers are likely timed.
2 heat, 3 heat, etc doesn't tell you how many stages of backup heat are supported.
The Following User Says Thank You to user_12345a For This Useful Post:
form8829 (01-06-2016)
Old 01-11-2016, 08:23 PM   #10
Rewards Points: 138
beenthere, did as suggested, went through installer setup and no heat air came out. any more suggestions? this should be installer manual:
https://customer.honeywell.com/resou...0s/69-2668.pdf
Old 01-11-2016, 08:25 PM   #11
Rewards Points: 138
user_1234a, any suggestions?
Old 01-11-2016, 08:33 PM   #12
An old Tradesmen
You have 170 set to 7? And 180 set to 1?
Old 01-11-2016, 08:53 PM   #13
Rewards Points: 138
170 set to 7, but the installer skips 180 and jumps to 200.
Old 01-11-2016, 08:58 PM   #14
An old Tradesmen
Some newer ones do. 200 is set to 0, correct.
Old 01-11-2016, 09:02 PM   #15
Rewards Points: 138
i am not really sure what is set to as from 170 jumps to 200. but looking at the manual it seems the bold portion is the default, so i am assuming it is.
i do want to mention that when i increase the temperature like 3 degrees hight that the set to, the aux comes on and then heat air comes out.
Unknown Terminal On Control Board justplumducky HVAC 2 03-29-2014 06:25 PM
Problem with board or thermostat? HoldonLiz HVAC 1 02-18-2014 06:09 PM
ICP HQ1085928TX fan control board burn up too often Malpopies HVAC 19 09-03-2013 08:19 AM
New control board or fix it? Bobeht HVAC 26 01-18-2012 03:03 PM
weathertron Mecury Thermostat VickiL HVAC 4 02-06-2011 04:32 PM