Ruud Furnace - Thermostat Calls For Heat Fan Comes In Right Away/no Heat - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 10-22-2009, 06:43 PM   #16
Checks out fine. Water heater and furnace share 1 flu
Paul1 is offline   Reply With Quote
Old 10-22-2009, 06:48 PM   #17
GC/Master Plumber/Mech
Rewards Points: 560
Do you have a volt meter?
Do you know what the pressure switch is?
The pressure switch is easy to locate. Off the inducer motor there will be a small rubber hose follow it to the switch
Take the DVOM and one lead to the furnace case the other lead touch each teminal of the pressure switch when there is a call for heat
You will need to set the meter to AC voltage. Voltage should be around 24 vac
John Wayne once said "Life is tough and it is even tougher if you are stupid"
Tempstar and Trane Dealer
Old 10-22-2009, 07:04 PM   #18
Hvac Pro
yuri's Avatar
Rewards Points: 1,800
Read the wiring diagram VERY carefully with a magnifying glass, there should be a list of those flash codes buried in the diagram.
Old 10-22-2009, 07:15 PM   #19
I don't have the meter your referring to but I unplugged both terminals to the pressure switch and plugged them back in turn the power on and the furnace started normal. It is now running. We'll see if it continues to operate normal.
Old 10-22-2009, 07:26 PM   #20
Hvac Pro
yuri's Avatar
DO NOT run the furnace that way!!! That pressure switch is a CRITICAL safety device. It proves proper draft thru the furnace. You can now get CO poisioning from improper combustion!! Check the venting for obstructions like Plumber said. You may have a problem with the circuit board . It should not start with the switch jumpered. Needs to see an open switch before it starts up.
Old 10-22-2009, 07:38 PM   #21
It's all hooked up correctly (the way it should be). Venting correctly. I have to wonder if the wires were somehow loose or not seating well. Pressure switch is plugged in correctly. Nothing unplugged or disconnected.
Old 10-22-2009, 07:45 PM   #22
Rewards Points: 560
I agree with Yuri to some degree
But, disconnecting the pressure switch may have knock loose what was causing the switch to stick
These switches are known for sticking and binding because of fine particles of lint or dirt
I would STRONGLY tell you to search either online or at a local HVAC contractor for this pressure switch and replace it.
On the switch there will be a part number and a number something like .38 inwc this number tells that it takes .38 inches water column to close the switch and the new switch needs to match if you go with a universal switch
Old 10-22-2009, 07:47 PM   #23
Hvac Pro
yuri's Avatar
Sorry for the excitement, I thought you jumpered them together. DIYers scare us at times. I have had to replace LOTS of those pressure switches. .3"WC I believe. Actually a Ruud ongoing problem with them set too low. Get a new pressure switch and thoroughly check the venting and chimney and buy 2 good CO detectors. One for your bedroom the other in the basement stairwell.
Old 10-22-2009, 07:53 PM   #24
thanks to both for your help. I will take your advice on replacing the pressure switch and I have 1 CO det and will buy another and put in the bedrm.
thanks again,
Old 10-22-2009, 07:58 PM   #25
Rewards Points: 560
Yuri,
If he jumped the two wire wouldn't he get a fault of pressure switch closed?
All the furnaces that I have checked out the control board needs to see an open circuit between cycles before it will allow furnace start up sequence.
Just curious we don't have alot of Ruud's around here and I'm not to keen on Ruud's. Granted all furnace start up squence's are basically the same just trying to learn more about Ruud's
Old 10-22-2009, 08:08 PM   #26
Hvac Pro
yuri's Avatar
I am not exactly sure what he is doing. I have seen a lot of Rheem/Ruud mids and they have problems with faulty pressure switches. Not to say that is the problem UNLESS the draft is checked properly with a manometer. Could be a cracked heat exchanger or chimney problem. ALL furnaces have to see an open pressure switch to prevent non-Pros from jumpering them and leaving them jumpered without realizing what they are doing. There are some different startup sequences. I believe that Goodmans have the rollout on the burner box directly wired to the gas valve and not the board and won't show a rollout code. Still safe though. It should show pressure switch stuck closed on startup and not allow any burner operation unless the board is damaged.
Read the $575 for 45 minutes post for a good laugh. Fangs and me are at it again.
Ruud Furnace issue grubslinger HVAC 16 09-14-2011 12:13 AM
Heat pump or high efficiency furnace moisheh HVAC 13 11-14-2010 11:59 AM
Wiring a RobertShaw 9870i to Gas Furnace & Heat Pump jerfer HVAC 11 12-21-2008 09:09 PM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 01:55 PM