Ruud Furnace - Thermostat Calls For Heat Fan Comes In Right Away/no Heat - HVAC - DIY Chatroom Home Improvement Forum
Old 10-22-2009, 05:12 PM   #1
Ruud furnace - Thermostat calls for heat fan comes in right away/no heat
I have replaced the limit switch in the heat chamber and reset all others. Still the same. Fan comes on right away but no heat.
Paul1 is offline   Reply With Quote
Old 10-22-2009, 05:24 PM   #2
GC/Master Plumber/Mech
Rewards Points: 560
Is the control board providing a flash code?
John Wayne once said "Life is tough and it is even tougher if you are stupid"
Tempstar and Trane Dealer
Old 10-22-2009, 05:26 PM   #3
Not sure how to read the lights
Old 10-22-2009, 05:31 PM   #4
Rewards Points: 560
It will flash - flash pause flash - flash pause and so on
Count the flashes and the seperator will be a two second pause and start again
Old 10-22-2009, 05:39 PM   #5
Lights... 1 yellow and 2 green
yellow flashes 4 times (slowly) and as the fan starts the yellow light flashes rapidly. Doesn't seem to have any 2 second brks
green lights come on and stay on.
Old 10-22-2009, 05:41 PM   #6
Rewards Points: 560
Can you post a model and serial number
Old 10-22-2009, 05:47 PM   #7
Rewards Points: 560
Usually on one of the furnace door panels there will be a code chart or the meaning of the LED's in the series they are flashing
Old 10-22-2009, 05:48 PM   #8
model # UGPH-07EAUER
Ser # DF5D302 F3594 6927
75000 BTU Natural Gas Ruud
Old 10-22-2009, 05:57 PM   #9
No led chart on the panels. a trouble shooting guide on the mother board panel but it's limited and doesn't address the problem I'm having. I don't have a book. Bought house 34 yrs ago. It was 10yrs old then.
Old 10-22-2009, 06:12 PM   #10
Rewards Points: 560
From some other sites I read that you are having a pressure switch problem
Check the flue for restrictions..bird nest, dead bird ect
You could also remove the flue from the furnace temporaly and try to start the furnace and see if it starts and runs
If the flue is OK then you will need to check the voltage to the switch in and out and then the pressure.
Pressure is measured in inches of water column and you will need a manometer to measure it.
Start with the flue
Old 10-22-2009, 06:13 PM   #11
Hvac Pro
yuri's Avatar
Rewards Points: 1,756
What type of thermostat do you have? Is it an older electronic type? It may be faulty. When this happens check with a volt meter from G to C and W to C. Should not have 24 volts from G to C as that starts the fan. Should have 24 volts from W to C. Looks like a 1994 RUUD with a newer board, the older ones had no LEDs.
Old 10-22-2009, 06:25 PM   #12
newtech's Avatar
Rewards Points: 164
You have a 44yr old furnace???
newtech is offline   Reply With Quote
Old 10-22-2009, 06:25 PM   #13
I had put on a new thermostat 4 yrs ago. thought that might be the problem so I put back on the old thermostat and the problem was the same.
is there a place on line that I can get the codes for the LED lights?
Old 10-22-2009, 06:27 PM   #14
Sorry... I bought the house 4 years ago... 2005
Old 10-22-2009, 06:38 PM   #15
Rewards Points: 560
check the flue please
Ruud Furnace issue grubslinger HVAC 16 09-14-2011 12:13 AM
Heat pump or high efficiency furnace moisheh HVAC 13 11-14-2010 11:59 AM
Wiring a RobertShaw 9870i to Gas Furnace & Heat Pump jerfer HVAC 11 12-21-2008 09:09 PM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 01:55 PM