It seems like everyone here is convinced it's got to be the flame sensing circuit, could it be something else? For example, could it be going into lockout due to the limit control tripping repeatedly (dirty filter?). Or any of a number of other things?
hatrabbit is offline   Reply With Quote
Old 01-03-2010, 11:54 AM   #17
Hvac Pro
yuri's Avatar
Rewards Points: 1,122
YES. He needs to sit with and run the unit with the lower cover off and tape the door switch closed and monitor the LEDS to see if it is tripping on the pressure switch etc. Cycle it on/off a couple dozen times and the problem usually shows up. Patience is a virtue in our biz.
Old 01-03-2010, 12:58 PM   #18
dbh
I have taken the door switch out along with the power switch...i have watched the LED's and have cleaned the AC coils along with the exhaust vent...now the exhaust vent was pretty dirty...but i am still having the problem...when the unit flames up i get two solid green lights and a blinking yellow...when the unit locks out or doesn't turn on i have one solid green and a blinking green until i reset the power to the unit.
dbh is offline   Reply With Quote
Old 01-03-2010, 01:08 PM   #19
Is there a chart in the furnace or on the doors showing what that light set means?
Not positive but I think there should be a metal cover over the black box holding the circuit board. I think the codes are listed on the inside of that missing metal cover
Old 01-03-2010, 01:20 PM   #20
dbh
Not that I can find...schematics is anot it.
Old 01-03-2010, 01:23 PM   #21
Model number should be on that label over where the gas pipe comes in. We can probably find the codes with a model number.
Old 01-03-2010, 01:56 PM   #22
Hvac Pro
yuri's Avatar
The yellow LED indicates low flame current when it flashes. The codes are usually in fine print on the electrical schematic or the instructions that came with the new board. That unit has a history of pressure switch tripping problems. Sit there with your multitester on the switch and see if you get 24 volts across which indicates it has tripped. Cycle it 2 dozen times. Check the port on the inducer fan where the switch hose attaches for blockage, clean it with a small bit or paper clip.
Old 01-03-2010, 02:50 PM   #23
dbh
Model number is ugdg 10 eamer
Old 01-03-2010, 03:05 PM   #24
dbh
I Get 28 volts across the pressure switch when the unit is cycled off..two green solid LED`s ...unit turns on voltage at switch goes to 7mv then to 24mv...still getting the blinking yellow LED.
Old 01-03-2010, 03:10 PM   #25
dbh
Can not find the paper work that came with the mother board for error coding. i still have the box the control board came in and it is part number 62-24084-82 Protech
Old 01-03-2010, 03:37 PM   #26
Hvac Pro
yuri's Avatar
Did you clean the flame sensor with some fine emory paper/steel wool and the face of the burner it sits in front of? If not do so. There needs to be proper grounding from that circuit board to the chassis of the furnace. Some of those boards had a ground screw or wire and that may be loose/missing?
Old 01-03-2010, 04:44 PM   #27
dbh
After pulling the burners out and cleaning them and the flame sensor and everything else i could see i get a solid yellow when unit is operating....so hopefully that was it...thank you all for your help...here's to a warm house.
Old 01-03-2010, 08:48 PM   #28
Thumbs up
...Or, you can go online or call the manufacturer with the model # and they will send you all the relevant information. (No matter what) Don't Drink and Drive, ever!!!
spark plug is offline   Reply With Quote
Old 01-03-2010, 08:51 PM   #29
Cool
that model # sounds like it came from outer Mongolia or some other place in the now defunct, former USSR!!
Old 01-04-2010, 08:52 AM   #30
dbh
That would explain a lot SP...24hrs and no lock outs...
Old Silver-Line furnace problem avro1 HVAC 9 03-18-2010 01:01 AM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 02:55 PM
Carrier Furnace Problem Boats1183 HVAC 1 11-11-2008 07:41 PM
another question for a miller furnace problem jb9270 HVAC 1 02-05-2007 03:04 PM