Ruud Furnace Draft Inducer Fan Does Not Come On - HVAC - DIY Chatroom Home Improvement Forum
Old 11-09-2008, 01:45 PM   #1
Hey friends, I have a problem with my Ruud 90 series furnace. The model number is UGEB-19EE-GS.
The problem is that the furnace calls for heat and the only thing that happens is the blower motor comes on. Normally, the draft inducer motor will come on first then it will go through its normal sequence.
I can shut off power at the breaker panel, turn back on and the furnace will sometime work correctly.
Does anybody have an idea? Thank-you
Little Joe is offline   Reply With Quote
Old 11-09-2008, 03:06 PM   #2
Could be 2 or 3 things: bad board, bad inducer, bad electrical connections. If you have a volt meter- something that will read ac voltage not a wall tester, check for voltage at the inducer molex plug coming for the board. If you don't have voltage the board is bad if you do the inducer is bad, at least typically.
sgthvac is offline   Reply With Quote
Old 11-09-2008, 08:28 PM   #3
30 year tech
hvac122's Avatar
Sounds like a open limit to me. Check the safety circuit.
hvac122 is offline   Reply With Quote
Old 11-11-2008, 06:10 PM   #4
Thanks for the help, changing the board was the fix.
Ruud Furnace issue grubslinger HVAC 16 09-14-2011 12:13 AM
How do I test my draft inducer? ryansturmer HVAC 9 10-20-2008 07:41 PM
Draft Inducer question hvachelp HVAC 3 06-17-2008 04:40 PM
trane furnace with inducer blower error tjh57 HVAC 1 10-22-2006 07:45 PM