Model UPLB-048JAZ condenser
Model UBHK-24 air handler with RCHA48A1 inside coil
Inside coil with txv and .157 piston.
Outside condenser with fixed orifice.
Parts replaced by service tech last year: Inside coil and txv. Outside suction accumulator. New dryer. System was charged as per chart on outside condenser which considers outside ambient temperature and suction line temperature. Three years ago the outside condenser coil was replaced. The static air pressures are in the normal range.
The AC mode works flawlessly. The heat mode in this video will show you that the two lines going into and coming out of the suction accumulator are much more than 3 degrees. I will be presenting this to a RUUD representative but wanted to see if this can finally be resolved by one of the techs on this forum.
carlb7 is offline   Reply With Quote
Old 10-03-2011, 11:48 AM   #2
JJboy's Avatar
dude, you have this "problem" since 2008 ..... REPLACE YOUR SYSTEM
http://www.youtube.com/watch?v=_e8k_..._order&list=UL <==2008
http://www.youtube.com/watch?v=dF7nG..._order&list=UL
http://www.doityourself.com/forum/ar.../t-374532.html
http://hvac-talk.com/vbb/showthread.php?t=187977
Txv
Please check these links
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
Old 10-03-2011, 07:06 PM   #3
I wish I just had the money to plunk down on a new system. Yeah, this has been going on a long time and yet still no answer to the problem. We will see what RUUD says and maybe it will help some of the techs for the future.
Old 10-03-2011, 07:35 PM   #4
JJboy's Avatar
I can't wait to see the final of this case. Make it quick to get to the point not to lose the warranty, since this problem started in 2008. Being without heat for 3 season sucks.
Old 10-03-2011, 10:15 PM   #5
I think you have the wrong accumulator. A standard accumulator cannot be used in a heat pump application. The standard accumulator uses a larger size orifice, than a heat pump model. The smaller orifice in the heat pump model prevents liquid from exiting the accum during heating operation.
Master of Cold is offline   Reply With Quote
Old 10-03-2011, 10:30 PM   #6
JJboy's Avatar
I'm trying to kill this post ..... Do you think OP really doesn't have heat for 3 season.....I don't think so.
Easy fix ==> REPLACE UNIT. Call the Mater, super, kick ass RUUD PRO technician or pray a lot.
Old 10-03-2011, 11:00 PM   #7
I'm Your Huckleberry
Rewards Points: 2,270
Does Op realize that a suction line drier must be removed especially on heat pump? And that high side should be bi-directional, and probably changed as well. I think he needs to have refrigerant recovered, suction drier removed, line set triple evacuated and finally re-charged.
Doc Holliday is offline   Reply With Quote
Old 10-03-2011, 11:01 PM   #8
This is not a Ruud problem, this is an install problem.
Me thinks, anyways.
Old 10-03-2011, 11:21 PM   #9
JJboy's Avatar
I guess coils are not matching
Old 10-04-2011, 07:40 AM   #10
Settle down rookies..I told you the problem.
Any goofball can tell him to replace it. As a tech your job is to repair it, not throw it away after 3 yeats.
Old 10-04-2011, 11:29 AM   #11
I think you have the wrong accumulator. A standard accumulator cannot be used in a heat pump application. The standard accumulator uses a larger size orifice, than a heat pump model. The smaller orifice in the heat pump model prevents liquid from exiting the accumulator during heating operation.
This is very interesting Master of Cold. It makes perfect sense. I will do some research and see what is presently on my system.
I talked to the RUUD tech help. Their explanation was that it is working as designed. That in Heat Mode the system requires more refrigerant than AC Mode and that the suction accumulator was supposed to frost up as well as the outlet tube to the compressor. They say that I will get many "opinions" on the matter but that is because they do not know how the RUUD system is supposed to operate.
I will give you the model number of my accumulator and let you know what I have. Also thanks for not "killing" my post.
Old 10-04-2011, 12:24 PM   #12
Parker Suction Accumulator Model PA5083-12-7C.
Old 10-04-2011, 12:26 PM   #13
JJboy's Avatar
So .... the system is working as it should be ......
Old 10-04-2011, 12:40 PM   #14
If you believe the RUUD tech .........
I have more faith in Master of Cold.
Is there something I have done to upset you JJboy? I didn't mean to offend you. I thought this was a forum for information, not to belittle the poster.
Old 10-04-2011, 12:55 PM   #15
JJboy's Avatar
Of course not. I think you're worrying about something that is functioning normally, as the RUUD said. After 3 years with your system working in this condition and you still think that a problem.
Ok, since this symptom is normal ...... What is the problem again?
Ruud vs Trane peter_holmes HVAC 23 07-28-2010 02:32 PM
Ruud heat pump high pressure switch mikethe ductman HVAC 3 07-28-2010 06:00 AM
Ruud help tritrinh HVAC 3 12-05-2009 10:47 PM
Help: All I wanted to do was replace a light switch MicahPDX Electrical 5 07-04-2009 12:13 PM
Ruud a/c control board replacement ? kourso HVAC 1 07-20-2006 09:33 PM