RTH8500 Themostat...AC Blowing Warm Air - HVAC - DIY Chatroom Home Improvement Forum
Old 04-05-2009, 07:56 PM   #1
RTH8500 Themostat...AC blowing warm air
Outside Unit: Carrier 38ycc030300
Airhandler: FA4ANF030000AFAA
Old T-stat: Bryant TSATBBNHP01B
Problem: Replacement thermostat blows warm air for AC. Heat is working just fine with the heat pump.
First time visitor. Here is the wiring:
Red Wire to R
White wire to O/B (based on config on old Bryant t-stat which was W/W1)
Blue wire to C
Green wire to G
Yellow wire to Y
Orange wire to Aux (O/W2 on Bryant Tstat)
Setting on program for function 170 to 9 (2 heat 1 cool).
I also re-mounted the old thermostat and the cool works fine, so the problem is not with the heat pump/AC unit...the problem is either in my wiring or the programming. Also, there is a brown and a black wire which were not attached to any place in the old thermostat. Any suggestions will help. Thanks
jtsliders is offline   Reply With Quote
Old 04-05-2009, 08:41 PM   #2
An old Tradesmen
Rewards Points: 6,116
W1/O of new stat, is same as W2/O of old stat.
You have it wired wrong.
Old 04-05-2009, 08:51 PM   #3
OK...I checked it out and I was mistaken...the white wire is on O/B on the new thermostat. I even tried swapping the orange and white wires...same result...warm air.
Old 04-05-2009, 08:57 PM   #4
An old Tradesmen
The orange wire goes on to the O/B terminal(pressuming its also attached to the O terminal at the HP). Which is a common wiring config for heat pumps.
You also must tell the stat its controlling a HP, and that O is energized in cooling mode.
Sometimes you have to read the install instructions several times.
And some of those cheap thermostats come wth really crappy install instructions.
Old 04-05-2009, 09:06 PM   #5
On the old thermostat, the orange wire went to the Aux heat...so you are saying on the new one,
1. I need to connect the orange to the O/B?
2. Then, will the white wire go to the aux?
I tried 1 and 2 with the same result. This whole "Easy to install" thing is frustrating the crap out of me. BTW...thanks for your quick replies.
Old 04-05-2009, 09:15 PM   #6
An old Tradesmen
You said on the old stat the orange wire went ot O/W2.
Since it had a O designation also, that means it was a RV control terminal, or an aux heat terminal, depending on configuraion se up.
W1/O on teh new stat is what controls the RV*reversing valve)
W2 of the new stat is aux heat.
White wire is generally aux heat.
Old 04-05-2009, 09:19 PM   #7
No W1/O on the new one...it is an O/B (I changed the original post). So, what is your suggestion on the proper wiring? Thanks.
Old 04-05-2009, 09:25 PM   #8
An old Tradesmen
Red Wire to R
See her where white wire was on aux terminal of old stat. W/W1 is aux heat.
Blue wire to C
Green wire to G
Yellow wire to Y
See here where you say the old stat had a O/W2 terminal.
The O is always a RV control terminal, on residential equipment.
The orange wire belongs on the W1/O terminal of the new thermostat.
The white wire goes to the W/2 terminal.
Old 04-05-2009, 09:27 PM   #9
Yes...I muddled the initial post...and did not change it until after you responded. There is NO W1/O terminal (my mistake, again)...it is O/B (for Heatpumps) and W (for conventional).
Old 04-05-2009, 09:42 PM   #10
An old Tradesmen
O/B is what the orange wire hooks to.
Old 04-05-2009, 09:55 PM   #11
OK...one last try tonight.
1. I connected Orange to O/B
2. White to the Aux...and also (per page 12 in the installation guide,
3. connected a small jump wire to the E terminal...If E and Aux terminals do not each have a wire connected, use a small piece of wire to connect them to each other.
Waiting for the AC to cycle on...and...nice WARM AIR coming out.
Thanks for trying to talk me through this. I will be calling the local Carrier dealer tomorrow.
Old 04-05-2009, 09:57 PM   #12
An old Tradesmen
Did you go into the set up menu, and tell it to energixe the O terminal in cooling mode.
Old 04-05-2009, 10:01 PM   #13
An old Tradesmen
PS: 170 must be set to 7.
Other wise, it won't know that your hooking it to a heat pump.
And 190 must be set to 0(zero).
Old 04-06-2009, 06:09 AM   #14
I will try that setting today when I get home...and duh...9 is CONVENTIONAL. Like you said...read the directions CAREFULLY.
(Edit...it seems to be working, with the jumper wire going from the Aux to the E terminal). Thanks so much for your help...and most of all...for your PATIENCE)
Old 08-29-2015, 02:36 PM   #15
Rewards Points: 2
Thank you!!!
I know this is an old post/conversation, but I was struggling with same problem. Thanks to this chat, I was able to trouble shoot the problem and save a technician fee.
THANKS!!!
luiszo is offline   Reply With Quote
Tags
honeywell rth8500 , thermostat installation
RTH8500 Wiring O and B Terminals dermanj HVAC 19 06-05-2016 03:55 PM
A/C not blowing cold air... rnorred13 HVAC 9 04-03-2014 04:03 AM
HEIL/ICP gas/electric self-contained unit -- blowing cold air, won't shut off AboveTheBULL HVAC 3 06-28-2010 07:23 AM
Registers are not blowing air Macgyver HVAC 6 01-19-2007 03:39 PM
my tile floor is warm minahanna Plumbing 8 01-23-2006 07:04 PM