-   -   RTH8500 Themostat...AC blowing warm air (http://www.diychatroom.com/f17/rth8500-themostat-ac-blowing-warm-air-41876/)
jtsliders 04-05-2009 07:56 PM
Outside Unit: Carrier 38ycc030300
Airhandler: FA4ANF030000AFAA
Old T-stat: Bryant TSATBBNHP01B
Problem: Replacement thermostat blows warm air for AC. Heat is working just fine with the heat pump.
First time visitor. Here is the wiring:
Red Wire to R
White wire to O/B (based on config on old Bryant t-stat which was W/W1)
Blue wire to C
Green wire to G
Yellow wire to Y
Orange wire to Aux (O/W2 on Bryant Tstat)
Setting on program for function 170 to 9 (2 heat 1 cool).
I also re-mounted the old thermostat and the cool works fine, so the problem is not with the heat pump/AC unit...the problem is either in my wiring or the programming. Also, there is a brown and a black wire which were not attached to any place in the old thermostat. Any suggestions will help. Thanks
beenthere 04-05-2009 08:41 PM
W1/O of new stat, is same as W2/O of old stat.
You have it wired wrong.
jtsliders 04-05-2009 08:51 PM
OK...I checked it out and I was mistaken...the white wire is on O/B on the new thermostat. I even tried swapping the orange and white wires...same result...warm air.
beenthere 04-05-2009 08:57 PM
The orange wire goes on to the O/B terminal(pressuming its also attached to the O terminal at the HP). Which is a common wiring config for heat pumps.
You also must tell the stat its controlling a HP, and that O is energized in cooling mode.
Sometimes you have to read the install instructions several times.
And some of those cheap thermostats come wth really crappy install instructions.
jtsliders 04-05-2009 09:06 PM
On the old thermostat, the orange wire went to the Aux heat...so you are saying on the new one,
1. I need to connect the orange to the O/B?
2. Then, will the white wire go to the aux?
I tried 1 and 2 with the same result. This whole "Easy to install" thing is frustrating the crap out of me. BTW...thanks for your quick replies.
beenthere 04-05-2009 09:15 PM
You said on the old stat the orange wire went ot O/W2.
Since it had a O designation also, that means it was a RV control terminal, or an aux heat terminal, depending on configuraion se up.
W1/O on teh new stat is what controls the RV*reversing valve)
W2 of the new stat is aux heat.
White wire is generally aux heat.
jtsliders 04-05-2009 09:19 PM
No W1/O on the new one...it is an O/B (I changed the original post). So, what is your suggestion on the proper wiring? Thanks.
beenthere 04-05-2009 09:25 PM
Red Wire to R
See her where white wire was on aux terminal of old stat. W/W1 is aux heat.
Blue wire to C
Green wire to G
Yellow wire to Y
See here where you say the old stat had a O/W2 terminal.
The O is always a RV control terminal, on residential equipment.
The orange wire belongs on the W1/O terminal of the new thermostat.
The white wire goes to the W/2 terminal.
jtsliders 04-05-2009 09:27 PM
Yes...I muddled the initial post...and did not change it until after you responded. There is NO W1/O terminal (my mistake, again)...it is O/B (for Heatpumps) and W (for conventional).
beenthere 04-05-2009 09:42 PM
O/B is what the orange wire hooks to.
jtsliders 04-05-2009 09:55 PM
OK...one last try tonight.
1. I connected Orange to O/B
2. White to the Aux...and also (per page 12 in the installation guide,
3. connected a small jump wire to the E terminal...If E and Aux terminals do not each have a wire connected, use a small piece of wire to connect them to each other.
Waiting for the AC to cycle on...and...nice WARM AIR :censored: coming out.
Thanks for trying to talk me through this. I will be calling the local Carrier dealer tomorrow.
beenthere 04-05-2009 09:57 PM
Did you go into the set up menu, and tell it to energixe the O terminal in cooling mode.
beenthere 04-05-2009 10:01 PM
PS: 170 must be set to 7.
Other wise, it won't know that your hooking it to a heat pump.
And 190 must be set to 0(zero).
jtsliders 04-06-2009 06:09 AM
I will try that setting today when I get home...and duh...9 is CONVENTIONAL. Like you said...read the directions CAREFULLY.:jester:
(Edit...it seems to be working, with the jumper wire going from the Aux to the E terminal). Thanks so much for your help...and most of all...for your PATIENCE)
luiszo 08-29-2015 02:36 PM
Thank you!!!
I know this is an old post/conversation, but I was struggling with same problem. Thanks to this chat, I was able to trouble shoot the problem and save a technician fee.
THANKS!!!