Robert Shaw Unitrol LP Gas Valve - HVAC - DIY Chatroom Home Improvement Forum
Old 11-22-2011, 04:27 PM   #1
Mechanical Contractor
Does anyone know what the nominal ohm value of a good coil (with all conductors removed) would be?
Ballpark Range
What is the nominal voltage Mv required to open main gas valve. Pilot is on.
All other associated switch and safeties have been tested for proper operation
Thanks,
Bobby K
Tijeras,NM
Bobby K is offline   Reply With Quote
Old 11-22-2011, 04:38 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 176
400 millivolts minimum but most of the time you need at least 500-600 from the generator (unloaded)due to the wiring and connections/loss etc.
Old 11-22-2011, 05:19 PM   #3
Thanks Yuri
Yuri,
Thank you for your answer. I will be installing a new T-Pile this evening, i will record its resistance and maximum MV generated at start up.
Any thoughts on the ohm value of the gas valve?
Happy Thanksgiving
Bobby K
Old 11-22-2011, 05:43 PM   #4
Hvac Pro
yuri's Avatar
Rewards Points: 176
Make sure the pilot burner is clean/clean orifice so that the flame surrounds the generator properly. After that it should produce 700 or more Mv when new. I worked on hundreds of those old units back in the day and never ohmed the gas valve. 99% of the problems are weak generator, dirty pilot, loose wiring connections, corroded connections on the valve or bad tstat. Must have absolutely bare copper wire when making connections on millivolt systems. Gas valves usually just die and stick closed.
On some of those universal generators there is a brass sleeve (Honeywells) and it can rob heat from the generator and needs shortening if using in a PG9 pilot burner to replace the fat PG9 which is not available or very hard to find.
Old 11-22-2011, 06:21 PM   #5
You Da Man,
Thanks again, I'll let you know how things turn out
How to diagnose gas valve problems Nestor_Kelebay How To Guides 28 10-30-2013 04:19 PM
pressure relief valve is leaking on boiler wlmpdiycr HVAC 65 10-26-2011 05:00 PM
Remove Robert Shaw D34000 Thermostat? wanderlust HVAC 7 10-11-2011 04:27 PM
Best 1/2 inch water shut off valve. Nestor_Kelebay Plumbing 10 07-25-2008 11:16 AM