Hi, first post here, hopefully I've collected enough detail to make a good start narrowing the problem. I'd be grateful if someone could pass along any specific info about operation of this controller beyond the brief bit on the labels, further troubleshooting steps, or anything at all that might point me in the right direction. I tried the Rheem site and they show no documents at all for this part number(or shortened variants of the part number). All troubleshooting info I have been able to find focuses on a failure of the unit to provide heat, which is the one thing it does right.
Symptom: When I try to manually activate the fan via the t-stat, there is a "click" from the control board but the fan does not actually start. When the t-stat calls for heat, everything works as it should. The burner lights, the fan blows, etc.
I'm pretty handy and should be able to perform any reasonable test. I suspect a bad relay but it doesn't make sense to me that there would be one relay for manually activating the fan and another for operating the fan when heat is called for. I would like to get some expert advice before tearing in and testing the relays for correct operation(e.g. apply 24v to coil & check contact operation). I found a replacement board online and after seeing the price I'm hoping it's something simpler.
OK, some details would help, eh? Note that we bought this house earlier this year so I have no history on this unit. BTW it's a horizontal unit.
Furnace:
Mfg: Rheem
Model: RGLG-07NAUER
Serial: CU1D302 F0893 6421
Converted with kit EP70H so now is model RGLG-07NAUET per the conversion label, though I doubt this relates to the problem -- I put a similar label on my gas dryer when I converted it to propane, all I did was modify the burner and replace the gas valve.
T-stat:
Mfg: Honeywell
Model: TH8110U1003
Serial: 302001000622252
Manual available @ bottom of page
here.
Here is a shot of the circuit diagram inside the unit:
(Click for larger size)
T-stat wiring at control board:
T-Stat wiring at T-stat(Note, I added the blue jumper after reading the Honeywell manual, no help):
This relay looks like it's been a bit hotter than intended. Also, I can't figure out from any of the info attached to the furnace what the DIP switch is for.
I've posted a few more photos
here, larger sizes are available from the small flyout menu that appears when you mose over a photo at that link.