Return Duct Size - HVAC - DIY Chatroom Home Improvement Forum
Old 02-16-2008, 03:37 PM   #1
return duct size
we live in a ranch house and converted our garage to a bedroom.the room is 272sqft.I am going to run a 6&7" round supplies,on the return would it be ok to run a 10" round duct from the trunk and once in the room "t" off 6&7" pipes?
dave150 is offline   Reply With Quote
Old 02-16-2008, 07:30 PM   #2
I'm assuming you are using Flex duct. If you are, you are better off over sizing the both the supply and the return. Flex dust reduces the amount of cfm that can pass thru. 6" metal pipe is rated at 100cfm 6"flex is rated around 75cfm to get the airflow you desire run 7" flex for the 6" and 8" for your 7"supply and return.
sgthvac is offline   Reply With Quote
Old 02-17-2008, 05:18 PM   #3
I am using metal pipe but the bedroom is on a slab which is seperste from the house so feeding a 6&7" ducts would be more difficult than to run one large pipe.so would feeding the 6&7" returns into a 10" running off of the trunk be ok?
Old 02-18-2008, 04:20 AM   #4
Yes, tieing your 6 & 7" will be fine to tie into 10" if you are running metal as you stated you must wrap the pipe with insulation because of heat loss in the winter and heat gain in summeer.
Old 02-20-2008, 02:19 PM   #5
i appreciate the feed back it is a HUGE help!!!! thanks again...
Should I seal return air duct? phareous HVAC 1 11-12-2007 11:14 PM
Central Air return duct location backpacker2 HVAC 3 05-28-2007 10:07 AM
Heater Return duct - Moved to HVAC forum backpacker2 HVAC 1 05-16-2007 11:30 AM
What size should cold air return grille be? AllGoNoShow HVAC 1 02-27-2007 03:48 PM