Replaced Thermostat....nothing, Need Help Please - HVAC - DIY Chatroom Home Improvement Forum
Old 06-05-2010, 02:40 PM   #1
replaced thermostat....nothing, need help please
My thermostat melted the other night, I replaced it, the furnace and fan would work but not A/C. Now nothing works.
I have power going to the unit in the basement from the heat side and the A/C side (from the circuit box). I have power at the AC unit outside. Where do I begin? Is the main circuit board the culprit? When I had a problem previously with the furnace, an indicator light was functioning, but now nothing is. I only see 1 fuse on the unit and that is on the heat side, fuse is good and there is power on both sides.
I am good around the house, but don't know where to start here? Circuit board is $150 or so, how do I troubleshoot this? I'm hoping its just a relay somewhere I'm missing.
diywhy is offline   Reply With Quote
Old 06-05-2010, 02:53 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 1,868
Why did the tstat melt? Did you have a thunderstorm/power surge/lightning? Post the make and model # of the furnace and some pics of it. Click on Go Advanced.
Old 06-05-2010, 03:03 PM   #3
No thunderstorm. No tripped breakers/blown fuses. It is amana air command 95 furnace and amana AC.
Old 06-05-2010, 03:19 PM   #4
Hvac Pro
yuri's Avatar
You should get 24 volts between R and C terminals on the circuit board. What literally happened to the tstat/melted?
Old 06-05-2010, 03:35 PM   #5
I just did this
ran blower wire to direct power (around circuit board) and the blower motor ran fine.
Old 06-05-2010, 03:46 PM   #6
The thermostat melted a hole in the back. I don't know if the wires touched and arced or what? Right now I have the fan running by bypassing the circuit board. I can replace the circuit board, I just want to know if I can possibly test other switches/controls to replace them and not the entire board. Also, how can I ensure that the same problem won't happen again?
Old 06-05-2010, 04:05 PM   #7
Hvac Pro
yuri's Avatar
Do you have 24 volts between R and C, follow our instructions carefully we are Pros.
Old 06-05-2010, 04:06 PM   #8
at the thermostat or on the circuit board? I have to find my multimeter and will check
Old 06-05-2010, 04:31 PM   #9
Hvac Pro
yuri's Avatar
At the circuit board.
Old 06-05-2010, 04:31 PM   #10
never heard of a stat melting on a wall. if you jumper y
to r do you get cooling or jumper r to w do you get heat r to g should give you fan. on some furnaces no ground to unit will fry board did you check transformer for 110 on line side and 24 volts on low side?
denver dog is offline   Reply With Quote
Old 06-05-2010, 04:47 PM   #11
Rewards Points: 85
Unhook t-stat from control board
Makesure you have 24 volts @r&c
jumper r-g=fan should come on
" r-w=heat"""""""""""""""""
" r-y=cond."""""""""""""""""for cond. to work cond common needs to be hooked up and pump or pan safety switchs need to be closed or bypassed"
I take it you already have high voltage since you got the fan going but it never hurts to make sure its the right voltage
If you have high&low voltage and none of the jumpers worked then it looks like the board
BTW If your t-stat melted there is a good chance your t-stat wire is shot too.
mikethe ductman is offline   Reply With Quote
Old 06-05-2010, 04:53 PM   #12
just tested R and C at the thermostat and on the board. no voltage.
Old 06-05-2010, 05:12 PM   #13
Rewards Points: 85
Now check the transformer and make sure if the furnace has a fuse on the control board that it is good too.
Old 06-05-2010, 05:15 PM   #14
I have no power from where my AC low voltage connects in with the high power.
Old 06-05-2010, 05:30 PM   #15
Rewards Points: 85
Does your blower door have a kill switch?
High voltage shoulg go through an on/off switch through the blower door kill switch then to control board and t-fromer.
Test high voltage at all 3 places, if thumbs up then sounds like bad t-former but ohm it out to be sure.
Pilot on Williams millivolt wall heater goes out every 8 to 16 hours wornways HVAC 30 06-22-2011 03:29 PM
Carrier Edge Thermostat Installation Issue ptalar HVAC 1 07-13-2010 05:40 PM
Problem with Lennox Pulse Furnace Wiring to Thermostat scalvin Electrical 4 12-30-2009 07:48 PM
Thermostat wiring jetmanaz HVAC 1 08-09-2009 07:13 PM
ac/furnace runs whatever thermostat settign donbohn HVAC 1 06-20-2009 05:42 AM