Just had our first annual maintenance on our new HVAC systems.
Equipment (upstairs)
Rheem RASL-024-JEZ condenser, RCFN-2417 coil, RGJD-06EMCK furnace.
Pressures 140/250 at 95 degrees/90% humidity (outside), 76 degrees inside 20 degree delta. R-410 refrigerant.
Equipment (downstairs)
Rheem RASL-036-JEZ condenser, RCQD-3621 coil, RGJD-07EMCK furnace.
Pressures 130/295 at 95 degrees/90% humidity (outside), 76 degrees inside 20 degree delta. R-410 refrigerant.
The tech proclaimed them "normal". Is it possible to confirm if these numbers look good?
Keith
sktn77a is offline   Reply With Quote
Old 06-22-2010, 10:10 PM   #2
They look a little low on the high side but other factors could be in play. I wouldn't worry about it. Did the tech measure superheat/subcooling?
Delta T looks OK as long as you have good airflow.
Have you noticed any change in the system's performance?
hennyh is offline   Reply With Quote
Old 06-23-2010, 05:44 AM   #3
An old Tradesmen
Rewards Points: 7,372
Your second floor high side reading can't be right(or you got a problem).
R410A at 250PSIG is a saturated temp of 83.6. That would be under the 95 outdoor temp you posted. If it is right, then there is a restriction before the point where he took the temp reading.
Other unit's sat temp is just above outdoor temp. Doubt its a correct reading either.
His gauge may be having troubles.
As above. Without SC and SH readings. Those readings don't tell us much.
Old 06-23-2010, 06:07 AM   #4
sktn77a's Avatar
Rewards Points: 392
Yes, I thought the high side pressures looked a little low for R410a (which is why I posted them here). The systems are working fine - no problems, no changes. He didn't measure (or at least he didn't report) SC and SH.
Keith
Refrigerant Charging Scale benjamincall HVAC 14 07-13-2014 06:10 PM
Why move/replace heat pump refrigerant lines? EdLank HVAC 1 05-09-2010 05:02 AM
new ac unit leaking refrigerant foxsam HVAC 16 12-15-2009 12:53 PM
HVAC flow rates and pressures. Cunning install ideas? viper HVAC 24 08-09-2009 12:22 AM
Refrigerant Level zpm HVAC 10 07-02-2009 07:36 PM