Ready To Pull Hair Out - HVAC - Page 3 - DIY Chatroom Home Improvement Forum
Old 02-16-2010, 07:31 PM   #31
Hvac Pro
yuri's Avatar
Rewards Points: 114
The unit may have been used/yanked from another house/oversized or who knows what if they did a sloppy job on the venting. Serious damage can occur in a short time from overheating and like Beenthere said, some guys increase the limit control rating and other BS to try keep units running. Without a crystal ball you never know what happened. I know what you are going thru. Learned EVERYTHING the hard way myself. Had no internet buddies to help either.
Old 02-16-2010, 07:38 PM   #32
An old Tradesmen
Rewards Points: 7,802
Boy.
The internet and forums like this would have made life SOOOOO much easier if it had been around like this in the 70's.
Old 02-16-2010, 08:20 PM   #33
Hvac Pro
yuri's Avatar
Rewards Points: 114
I bet you have a few "8 tracks" with Bee Gees stashed away from the good Ole days.
We had a "Disco Inferno" in the peg for a few years, Yuck.
Old 02-16-2010, 08:22 PM   #34
Just throwing one more thing out there, is it possible that the blower is not turning on fast enough, would that allow to much heat to throw the switch. There is a reason I ask. I should have mentioned this before, but I noticed some smoke coming out of the circuit board on what looked to be a relay and it didn't start smoking until the board called for the blower to come on. I tried switching the wires on the taps ex. black wire was on cool and I put it on heat and thats when I first noticed the smell and the smoke. I then switched the wires back and it did the same thing. I got so wrapped up in describing what was going on that I forgot to add that in. Sorry about that.
Livewire78 is offline   Reply With Quote
Old 02-16-2010, 08:49 PM   #35
Hvac Pro
yuri's Avatar
Rewards Points: 114
The blower normally starts after 45 seconds on a timer in the board. What happened, who knows? You need to check the temp rise thru the unit etc. If the board smoked then the unit is REALLY sick and it sounds like it is seriously damaged. Try get the serial # and find out the exact age of it. If you can prove to the customer it is oversized etc then maybe you can sell them a new proper sized unit and a B Vent for the chimney and have the whole unit work properly.
Old 02-16-2010, 10:11 PM   #36
An old Tradesmen
As Yuri said. The blower is on a timer. So it comes on when it should.
Even if you saw smoke come from the board.
Before you do anything else.
CHECK the heat exchanger. No one will be happy with lots of parts. And then find out the heat exchanger is shot.
And then end up being stuck with changing out a heat exchanger in an oversized furnace. And having it burn out in 2 or 3 years.
Old 02-16-2010, 10:17 PM   #37
Your probably right, I beginning to think that I'm trying to put a bandaid on a broken leg. Thanks for the advice on everything.
Old 02-21-2010, 09:51 PM   #38
No. Don't lower the manifold pressure. Causes other headaches.
Clock meter like Yuri said.
The furnace is more likely then not, grossly oversized.
The duct system is undersized.
If you can't get them to replace that furnace with the correct size.
Then make the duct work and supply registers and grille corrections needed to make that furnace safe and usable.
Take the temp rise across the heat exchanger. Suppose that its inputing 100,000BTU and giving you 80,000BTU out.
If its moving 1140CFM, then your temp rise is 65. Which gives you about 5 of safety before exceeding max allowable temp rise.
If your temp rise is above 70, its too high.
Output BTU divided by (temp rise times 1.08) equals CFM.
EG: 80,000/(80X1.08=86.4)=926CFM
The temp rise alone would be too high. But, you would know the CFM its moving. And be able to determine how much more air it needs to be able to move to be back at safe temp rise.
PS: What size house is this furnace in?
What is the easiest way to check gas vent to see if its clogged? The furnace was installed about 2 years ago and ran perfect until recent problems, I can feel the heat radiating off of the inshot burners before the blower starts.
Old 02-22-2010, 03:27 AM   #39
An old Tradesmen
Open it up and visually inspect it.
Also look inside inducer to make sure nothing is in it.
faucet hard to pull out? Leprichon Plumbing 14 11-15-2014 12:11 PM
Hog Hair Filter mjbxx HVAC 10 04-10-2009 08:46 AM
konecto prestige absorbing hair color dye 911 Robhen Flooring 9 03-03-2009 02:30 PM
No Pull lube jamiedolan Electrical 7 12-16-2008 12:00 PM
Hair in tub drain danceken Plumbing 5 05-24-2007 08:53 PM