Raypak Boiler Pilot Light Problem - HVAC - DIY Chatroom Home Improvement Forum
Old 01-13-2012, 02:20 AM   #1
Rewards Points: 29
Raypak boiler pilot light problem
Replaced new thermocouple, but the pilot light still goes off every day, checked the gas outlet pressure 4.80" WC in the 2nd stage, is it right? or the gas valve need replace. Thanks.
Model: H3-0135R
Ballastar is offline   Reply With Quote
Old 01-13-2012, 03:11 AM   #2
how
Rewards Points: 1,100
Boiler pilots go out because of faulty thermocouples, bending of the copper line as it immediately exits the thermocouple body, incorrect thermocouple placement in the pilot assy, partially obstructed pilot orifices, anything that causes the cold junction of the thermocouple to overheat, pilot flames snuffed from concussive ignitions or shut offs, water dripping on the coupler, obstructed heat exchanger, faulty gas valve pilot solinoid, etc.
In the field a thermocouple tester (it's cheap) which allows a closed active measurement of the dcmv output of the thermocouple through a heating cycle is the usual diagnostic tool.
how is offline   Reply With Quote
Old 01-13-2012, 05:33 AM   #3
An old Tradesmen
Rewards Points: 6,464
Gs pressure sounds way too high.
Old 01-13-2012, 07:15 AM   #4
Rewards Points: 1,216
I agree recheck that gas pressure again.
After the main valve opens watch your pressure and adjust lower probably around 3 to 3.5 WC. Look on the heater doors and check the manuals that came with the unit they should instruct you how to adjust gas pressure and what the normal reduced pressure should be when main burners are on.
COLDIRON is offline   Reply With Quote
Old 01-13-2012, 11:42 AM   #5
how
All residential natural gas valves that I've seen have output press spec's close to 3.5" WC. The only time I've seen that kind of pressure from a gas valve has been when it's been broken, seriously miss adjusted by someone without a manometer or been hooked up to 2 lb gas. The first & second stage of your gas valve should only effect the gas volume, not the pressure.
If the pressure is that much higher on the second stage than the first, then something is wrong with that gas valve and I'd change it.
Only if the first & second stage are both putting out 4.8" would I consider reg adjustment.
If you are actually getting 4.8"WC, then that's way off base and I'm suprised that your furnace limit and roll out switches are not beating the thermocouple in shutting the furnace down.
The overheating of the cold junction of the thermocouple by an over fired furnace would be the probable reason the thermocouple is shutting down the furnace.
Old 01-13-2012, 01:18 PM   #6
Rewards Points: 29
The Gas control valve is from Robertshaw 004824F ( Nat. Std 2 stages)? I can not find where to adjust the gas pressure.
Pilot light button on furnace won't turn whydonchathen HVAC 8 01-19-2015 11:40 AM
Two 3-way switches: one pilot light, one regular flitz Electrical 14 08-20-2012 07:46 PM
Pilot light won't light BarryBe HVAC 3 05-22-2011 12:05 PM
Oil Boiler Pressure Problem soaddrummer HVAC 5 01-17-2011 06:56 PM