Random Flame Rollout On Gas Furnace - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 03-02-2012, 06:04 PM   #16
Originally Posted by yuri View Post
Depending on the model that furnace MAY NOT be approved for sideways/horz use and may be a serious fire hazard.
Its actually not. The installation manual calls for a vertical vent but I just assumed since it has a draft inducer you could side vent it....it was working fine for several weeks until this.
Doing some more research I think I have my terminology wrong. I was watching a bunch of youtube videos of flame rollouts and that is not what is going on. Well it is but ONLY on ignition and when the unit is hot and it doesn't happen all the time. I think what's happening is that the heat exchanger is building up gasses (maybe from the improper flue setup i have going on) and when it re-ignites the unburnt gasses mixed with fresh fuel and the igniter make it go 'poof'.
The model number is: 80MGF and it's a Lennox brand. The unit is hung horizontally and the flue exhausts 90* then goes 2' to the wall and through a thimble and out. I have another elbow and flue pipe I'm going to go put on right now and see what happens. I'll snap some pics and if I'm adventureous enough with my iPhone i'll take a video of what's happening and post it on youtube with a link for your opinions.
Thanks so Much for all the help!
Albe
Albe is offline   Reply With Quote
Old 03-02-2012, 06:27 PM   #17
hvac5646 is offline   Reply With Quote
Old 03-02-2012, 06:31 PM   #18
Hvac Pro
yuri's Avatar
Rewards Points: 116
Actually that is an approved multiposition furnace ( upflow, downflow or sideways, has nothing to do with the venting which our poster is talking about but not done properly anyway.). I checked the install info. Most are upflow only not multiposition. It sounds like it is cycling on the high limit control as there is not enough air going thru it and it is overheating. It SHOULD NOT go poof when starting as that is delayed ignition and could be from the improper venting. I suspect the burners need removing and clean the holes out carefully with a nail or pick and clean the slots. Then flush them thoroughly in hot running water and blow them out with compressed air. It must be vented properly for safety and legal reasons. If you go out the sidewall you have to run it up vertically above the roof line 3 feet and put a proper rain cap on too. Not my favorite Lennox furnace and actually is a pain in the arze to deal with. Has a basic not oversized blower. Builders grade furnace.
Old 03-02-2012, 06:42 PM   #19
He still has not stated why the guy he bought it from replaced it.
Old 03-02-2012, 07:09 PM   #20
Hvac Pro
yuri's Avatar
Rewards Points: 116
pain in the arze, probably got tired of fixing it or the cost of doing so. is at least 12-16 yrs old now.
Old 03-03-2012, 08:49 AM   #21
Figured out the problem! It had nothing to do with venting per se.
First off the OP only got rid of it because he had good incentive/rebates to get a new high efficiency unit.
When I first installed the unit it worked fine for weeks. After hooking up ductwork was when the problems started. Turns out a piece of insulation lining the heat collector box came loose and was blocking part of the heat exchanger this over heating the exchanger and when the unit would re-light it would go "poof".
So far so good but I'll keep ya'll updated if anything changes. Thanks so much for ALL your help.
Albe
Old 03-03-2012, 12:35 PM   #22
how
Rewards Points: 1,104
Aahhh. A wonderful example of the limits of remote communication and diagnostics..
how is offline   Reply With Quote
Natural Gas Cost For Furnace 1 Hour Run Time hammerlane HVAC 25 01-14-2015 02:13 PM
Flame rollout switch rmason HVAC 5 01-21-2010 07:36 AM
Lennox Merit Series Furnace - Flame Sensor?? dburell HVAC 3 12-29-2009 08:13 PM
gas furnace flame rollout Yoyizit HVAC 45 09-17-2009 08:06 PM
Coleman Furnace - Flame Goes OUT!!!! mmoniz HVAC 1 03-02-2009 09:23 PM