R-22 Beer Cooler - HVAC - DIY Chatroom Home Improvement Forum
Old 03-12-2014, 11:45 AM   #1
R-22 beer cooler
I am working on a 5 -ton R-22 beer cooler in a gas station. It trip on high pressure last night. When I checked the pressures they were low
low side 39.8
high side 193.5
low temp was 52.5
highr side temp was 94.3
Super heat was 38.2 and subcool was 4.8
Sounds low on charge to me. but what keeps tripping the high limit?
What Vsat should a beer cooler be run at? I was thinking maybe around 25 degrees?
actech is offline   Reply With Quote
Old 03-12-2014, 03:47 PM   #2
Rewards Points: 1,989
low side 39.8
high side 193.5
low temp was 52.5
Is air flow at the condensing coil OK ?
God bless
Wyr
WyrTwister is offline   Reply With Quote
Old 03-12-2014, 05:00 PM   #3
An old Tradesmen
Rewards Points: 7,368
What was the outdoor temp when you were checking it. If it was below 70 you may have a restriction in the refrigerant circuit.
Old 03-12-2014, 07:39 PM   #4
yes air flow is great at the outside coil 2 new fans. It was about 70 degrees outside. Why would you say restriction, low head pressure or high super-heat? I did add a little r-22 to get a better super heat, but when I did of course the vsat went up to 32 or so. I would think the coil definitely needs to stay below freezing. I can get it to 15 degrees superheat and 10 subcool, but that cant be right for a beer cooler the vsat would be 40 - 50?
Old 03-12-2014, 08:04 PM   #5
An old Tradesmen
Your head pressure is up high enough for temps of 70 degrees or less outside. You have a high SH. Indicates that the refrigerant isn't being fed to the evap as much as it should.
Old 03-13-2014, 08:36 AM   #6
I have 3 evaporator circuits with two fans on each. Do I need to check the supreheat at the backside of each individual evaporator to find out which one is restricted?
Old 03-13-2014, 09:02 AM   #7
Hvac Pro
yuri's Avatar
Rewards Points: 2,274
What turns on the condenser fans? A relay or contactor? Either way that could be intermittently sticking off and you have no fans.
Old 03-13-2014, 10:01 AM   #8
Fans run 24/7 it's med temp cooler
Old 03-13-2014, 04:36 PM   #9
An old Tradesmen
Yes. Anyone of them could be starved, while the other 2 are feeding as much as they can to maintain walkin temp.
Roof penetrations and other swamp cooler questions tylernt Electrical 11 11-16-2012 04:04 AM
Troubleshooting Fluorescent lights Servicewiz Electrical 5 07-11-2012 08:49 AM
Ground wire to pipe pisbouts Electrical 5 10-24-2011 07:45 PM
Removing swamp cooler control Pharmjae Electrical 3 02-10-2010 03:36 PM
Swamp cooler vents Summiteer HVAC 4 02-04-2010 04:59 PM