Old 06-15-2008, 06:03 PM   #1
Question Re: New Furnace and Duct Sizing
I am replacing a 50+ year old Natural Gas forced air furnace with a new 90+ efficiency "Hamilton" single stage forced air furnace model # WUN-100-4C. Both old and new furnaces are 100K BTU.
The new furnace outlet is the same size as the old, (19 3/4w x 20d) as is the plenum. The installation manual for the new furnace specifies a minimum return total size of 360 sq. in. and a minimum supply of 280 sq. in.
There are currently 5 ea. 6" round ducts from the plenum and 5 ea. 6" round ducts used for return air.
5 ea. 6" round ducts = 141 sq. in. Will I have any issues with this duct arrangement even though the old furnace used this duct arrangement for many years? If so, what can I do to resolve the issue/s?
This system will used for 3 ton central AC also.
DSimo is offline   Reply With Quote
Old 06-16-2008, 07:34 AM   #2
Another DIY Zombie
What is the size of the supply outlet of the furnace, and what is the size of your supply duct where it would connect to the furnace? That is the real question here.
I assume that this is a constant volume system, one zone?
javan is offline   Reply With Quote
Old 06-16-2008, 10:24 PM   #3
The outlet of the old and new furnace is roughly 19 1/2 x 20 inches. This is also the plenum size. Also, yes, this is a single zone system.
Old 06-17-2008, 08:24 AM   #4
Another DIY Zombie
I don't see where you would have any issues.
Tags
duct sizing
Gas furnace exhaust vent question nowell HVAC 7 01-30-2012 09:31 AM
Furnace sizing thumbkins HVAC 5 03-26-2008 09:05 AM
Connecting inline duct fan to furnace dlem HVAC 1 02-11-2008 06:50 PM
duct sizing Stu HVAC 2 12-22-2006 06:36 PM
Replace furnace, coil and duct system sps123 HVAC 2 01-07-2006 11:56 AM