Question for Beenthere


Been:

On the 'talk' forum, you replied to 'low amp draw' and asked if the WB temps were taken for supply and return to calculate actual capacity.

Could you elaborate, please, how that is done using those values?

Thanks.

V

Advertisement

veesubotee is offline   Reply With Quote
Old 06-05-2009, 05:50 PM   #2
An old Tradesmen
 
Join Date: Oct 2008
Location: PA
Posts: 26,414
Rewards Points: 4,480
Default

Question for Beenthere


You convert wetbulb to enthapy(BTUs per pound of dry air).
Then multiply the enthapy difference by the CFM and by 4.5 to get total capacity.

EG:

Return, 76DB 63 WB=28.477BTUs per pound dry air.
Supply, 56F DB 54WB=22.602BTUs per pound dry air.

28.477-22.602=5.875 Enthapy Delta.
5.875Enthapy DeltaX4.5Seal Level Constant=26.437X1000CFM=26,437BTUs total capacity.

Advertisement

beenthere is offline   Reply With Quote
Old 06-06-2009, 07:35 AM   #3
Member
 
Join Date: Nov 2008
Posts: 279
Rewards Points: 252
Default

Question for Beenthere


Quote:
Originally Posted by beenthere View Post
You convert wetbulb to enthapy(BTUs per pound of dry air).
Then multiply the enthapy difference by the CFM and by 4.5 to get total capacity.

EG:

Return, 76DB 63 WB=28.477BTUs per pound dry air.
Supply, 56F DB 54WB=22.602BTUs per pound dry air.

28.477-22.602=5.875 Enthapy Delta.
5.875Enthapy DeltaX4.5Seal Level Constant=26.437X1000CFM=26,437BTUs total capacity.
Thanks, Been
veesubotee is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Basement Renovation Question KUIPORNG Remodeling 234 08-26-2008 09:19 AM
hrv question indep HVAC 3 07-17-2008 11:39 PM
Basement vapor barrier question rob7young Remodeling 2 04-13-2008 10:10 AM
New service Question Onytay Electrical 1 10-24-2007 06:47 AM
One furnace question and one thermostat question lh0628 HVAC 4 10-11-2007 11:17 PM




Top of Page | View New Posts