Old 10-07-2011, 10:16 AM   #1
problem with concord 80 gas furnace
changed out honeywell gas valve and furnace worked great. Had a small gas leak and tightened up coupling. restarted furnace after rechecking for any additional gas leaks and it would not cycle through and was flashing 3 lights signalling pressure switch or auxillary limit stuck open. Looked at schematics and traced the violet wires down to the orange tubing checked tubing clear no water in it and could easily blow through it. Put tubing back on and again same signal. Any suggestions or helpful hints would be greatly appreciated! Thank You
djmanley is offline   Reply With Quote
Old 10-07-2011, 10:57 AM   #2
Check the opening going into the pressure switch. Take a piece of t-stat wirn and stick in the opening where the tube connects to the pressure switch. Sometimes these will clog.
Patrick Eubanks is offline   Reply With Quote
The Following User Says Thank You to Patrick Eubanks For This Useful Post:
djmanley (10-17-2011)
Old 10-07-2011, 01:34 PM   #3
will try that next and see what happens. If that doesn't work any other suggestions.
Old 10-07-2011, 02:08 PM   #4
JJboy's Avatar
Also check limit switch. Using multimeter in ohms you should have 0 ohms across the terminals
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
Old 10-07-2011, 10:24 PM   #5
Was the gas valve an OEM replacement or an universal type? I've had a call back on another techs GV change out, he used a universal and didn't check his outlet gas pressure on GV. GV putting out too much heat and tripping high limit. Adjusted pressure and I was good to go. No problems since.
thestig3 is offline   Reply With Quote
Old 10-10-2011, 11:42 AM   #6
I know this is going to sound dumb but looking at the schematics I can't figure out which is the limit switch. Could you describe where it is located and what it looks like? This would be of great help! Thanks
Old 10-10-2011, 11:58 AM   #7
I'm Your Huckleberry
Doc Holliday is offline   Reply With Quote
Old 10-10-2011, 12:00 PM   #8
In the first pic there is only one high limit switch, usually there are more than one tied in series.
Old 10-17-2011, 11:05 PM   #9
Talking
I greatly appreciate all the wonderful suggestions that was offered by all. The one from Patrick Eubanks is the one that did the trick I had tried this previously but not with that small of a wire and with his idea was able to get in there far enough to push what ever was in the opening on past and it is working perfectly now! Just in the nick of time as cold weather is moving in tonight! Thanks again
Heil Furnace Burner Problem timothyr HVAC 78 01-18-2013 07:49 PM
Help with furnace blower problem Spydey HVAC 6 12-15-2010 09:18 PM
Payne PG9YAB high efficiency 95% furnace water draining problem jchen64 HVAC 9 12-06-2010 07:42 PM
Old Silver-Line furnace problem avro1 HVAC 9 03-18-2010 01:01 AM
Strange Problem with My Furnace chenjijc HVAC 14 11-04-2009 10:05 PM