Old 08-19-2010, 03:11 AM   #1
PRO to PRO question.....
... on a new or replacement AC install, do you guys fuse the circuit at the cond as well as the line supply connection, or do you fuse only one end of the circuit and use a non-fused disconnect?
hvaclover is offline   Reply With Quote
Old 08-19-2010, 05:32 AM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 146
Breaker inside the house only. Fuses in OLD homes. Breakers in outside boxes eventually corrode and fail. If they trip then most customers don't know how to find them anyway. Pull disconnect at unit.
Old 08-19-2010, 06:34 AM   #3
I rarely see a fused disconnect.
Old 08-19-2010, 11:46 AM   #4
Craftsman
Depends on the length of the circuit to the unit, load, conductor and breaker size. On a long run (example rooftop units) when a problem occurs a breaker in the main panel will not react quick enough if at all. On long feeders using fuses or a breaker switch at the unit is good design
Superrick is offline   Reply With Quote
Old 08-19-2010, 01:35 PM   #5
I've seen jobs where the supply voltage is fused at the service panel
and a fused disconnect mounted at the cond. But no fuses...the installer used half inch plumbing cipper to jump the fused contacts....~sigh~ ...I hate hack jobs
Old 08-19-2010, 05:05 PM   #6
newtech's Avatar
Rewards Points: 164
I all ways use a fused disconnect at the condenser. It depends where the line supply connection is, if I will add one more disconnect. ( A meter tap for ex; I don't care if it is 3 feet away) it gets 2 fused disconnects... Off of a breaker box I will not add a second fused disconnect.
Hey for a few pennies for the disconnect and fuses. Why take a chance...
newtech is offline   Reply With Quote
Old 08-19-2010, 09:36 PM   #7
" Euro " electrician
frenchelectrican's Avatar
It depending on what the outdoor unit requirement some will listed fuse only so it have to be fused otherwise if say fuse/ HVAR breaker then I will just go with breaker in main panel and have unfused pullout on outdoor location.
The other gotcha some peoples are not aware sencie most of Electricians are aware with additional code is conveince repectale it have to be withen 25 feet of the outdoor unit.
Merci.
Marc
Old 08-19-2010, 09:38 PM   #8
I will be extra carefull if you say meter tap that is a very fine line to cross on that one and there are a bit of code on this one.
Most of the 100 and 200 amp resdentail meter socket are NOT rated for two conductors on the lugs unless it stated by manufacter.
Merci.
Marc
Old 08-20-2010, 02:53 AM   #9
Merci.
Marc
There is no restriction on tapping the meter.
Old 08-20-2010, 10:46 PM   #10
Really?
If you don't mind you quoute the NEC number that do allow this methold ??
Merci.
Marc
Old 08-21-2010, 12:32 AM   #11
Electrician
Proby's Avatar
I don't see how you could say that... Id certainly like to hear more
Anything fun is either illegal, immoral, or fattening.
Proby is offline   Reply With Quote
Old 08-21-2010, 03:16 AM   #12
Really?
Merc end
As concerns a single hook up of an AC cond. No, I don't know the NEC number. I am going by what the local authorities allow.
Old 08-21-2010, 08:07 AM   #13
Licensed electrician
Rewards Points: 1,766
Are the lugs rated for two conductors? Does the power company allow access into their socket to allow these connections to be made? Do you have the proper training and PPE to be working in a live socket?
Old 08-21-2010, 08:43 AM   #14
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
there is a serious (legal, as in NEC) restriction on tapping the meter. First, I know of no meters 200 amp or less that are designed to accept multiple conductors so you have that issue to deal with. Then, by NEC rules you must be able to turn off your entire electrical service from one point, even if you are allowed the 6 disco rule. So, if you tap the meter, you need to run it so the disco will be located next to the current main disco.
Then, since the AC disco is also a service disco, whatever you use as the disco must be rated to be used as "service equipment". Then, you need to comply with bonding requirements and grounding electrode connection requirements.
Of course, this is only in areas that follow the NEC though.
but as to the original question:
if this is a dedicated circuit, no fuses at the unit, just a disco.
The Following User Says Thank You to nap For This Useful Post:
Scuba_Dave (08-21-2010)
Old 08-21-2010, 08:50 AM   #15
Good points Nap. I can't think of any A/C disconnects that are rated as suitable for use as service equipment.
DRIcore question trailblazer1229 Flooring 0 02-24-2010 09:25 AM
3 Phase meter socket question a320200 Electrical 4 12-11-2009 12:45 AM
An unasked question is the only dumb question jackie treehorn Kitchen & Bath Remodeling 1 09-20-2009 08:24 PM
A question about water preassure. reasonforseason Plumbing 5 04-14-2009 04:36 PM
Basement Renovation Question KUIPORNG Remodeling 234 08-26-2008 08:19 AM