Pressure Switch Stuck Open? 2 Areas Im Looking @ - HVAC - Page 3 - DIY Chatroom Home Improvement Forum
Old 10-04-2012, 02:47 PM   #31
biggles's Avatar
might of been stuck OPEN...remove the 2 wires to the PS and set your ohm meter up to read open/closed start the IDM go CCW on that adjuster screw on the diaphram so the meter reads open with the IDM running go CW slowly till the meter closes(switch is closed)slight tweek to CW and it is set.that pressure switch has to be open before a call for heat and close when the IDM starts to prove there is air intro'd into the burner section so the rest of the show can go....any break in that closed contact during a heating cycle will shut the burner off(even if the IDM is running)and restart 3X then... latch out the furnace requiring a repower on the service toggle on the furnace....
Old 10-04-2012, 04:37 PM   #32
An old Tradesmen
Rewards Points: 6,586
Originally Posted by Cheloco51 View Post
So, thanks to all of you I was able to test/clean/check things out. My error code said that the switch was stuck open and when I sucked on the tube(or let the vacuum take over) everything fired up and worked fine. But after doing everything suggested it still wouldn't run on its own.
So bad pressure switch. When I took it off I noticed a screw in the middle of it. So I popped it off to find that it was holding a spring against the switch diaphragm. So I loosened it and put it back on and got the error code that the switch was stuck closed..hmm. I then tightened/loosened it until I got no error code and everything fired up/shut off properly.
So I guess that means that my pressure switch is pretty close to kicking the bucket. Just wanted to share my experience/fix since you have saved me a service call and taught me a ton.
Mahalo!
It has already kicked the bucket. Get a new one now. Cause you don't have a switch that will open when its suppose to, to protect teh furnace and you from harm.
Old 10-04-2012, 11:35 PM   #33
Yeah, I was planning on it since I didn't know how long this would last and it is a low cost fix. So what creates the pressure that opens/closes the switch? And could that be causing the issue?
Cheloco51 is offline   Reply With Quote
Old 10-05-2012, 05:25 AM   #34
An old Tradesmen
The inducer creates the pressure. It can be running slow. A 50 to 100 RPM drop is hard to see by eye or even hear.
Old 10-12-2012, 09:59 PM   #35
From what I've read the chances of it actually being the pressure switch are slim. Is that correct?
Also, would I be able to tell if the inducer wasn't creating enough pressure to trigger the switch properly without any equipment?
Old 11-30-2012, 03:28 PM   #36
Pressure switch keeps getting stuck open
I have a york diamon 90 and the pressure switch keeps getting stuck open. By blowing in the tube, it will reset the switch. Took combustion blower off of furnace, and ALOT of water came out, which fixed the problem for about two days. Did this again, and again it lasted for two days. What would be the reason water keeps filling up in there. I am completely stuck at the moment, and any advice would be appreciated. Thank you!
cpierce811 is offline   Reply With Quote
Old 11-30-2012, 05:00 PM   #37
An old Tradesmen
Could be a problem with the gas valve. Need to check the manifold pressure.
Old 12-01-2012, 08:44 AM   #38
How would I do that?
Old 12-01-2012, 08:47 AM   #39
An old Tradesmen
Need a manometer.
Old 12-01-2012, 02:59 PM   #40
Is there anything else that could be causing this to happen?
Old 12-01-2012, 07:32 PM   #41
An old Tradesmen
Obstruction in the flue/vent pipe, obstruction/dirty secondary heat exchanger, slow running inducer.
Old 12-02-2012, 11:53 PM   #42
The inducer motor seems to be running fine, no different than it ever has, how could I tell if the secondary heat exchanger was dirty or obstructed, and how would it be fixed?
Old 12-03-2012, 04:51 AM   #43
An old Tradesmen
Remove inducer and inspect it. Often it has to be replaced. Sometimes they can be cleaned.