Pressure Switch Failed To Close - HVAC - DIY Chatroom Home Improvement Forum
Old 03-07-2011, 08:31 PM   #1
Pressure Switch Failed to close
I have a York furnace. House has been getting colder and took off door, turned of automatic starter, waited the 5 minutes and then turned back on. Fan motor kicks on but no fire.
There is a flashing red light that flashes 3 times which cooresponds to "Pressure switch failed to close"; what does this mean and how is it fixed?
thanks in advance
bigdogtx is offline   Reply With Quote
Old 03-07-2011, 08:37 PM   #2
AKA HVACTECHFW
Rewards Points: 1,208
The small motor that is connected to the flue pipe has a rubber hose connected to the motor assembly. Remove the hose and ensure nothing is in the port on the motor assembly. it there is, try to remove it with a paper clip or small drill bit (with the power turned off). Does that motor run?
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 03-07-2011, 08:41 PM   #3
Yes that motor kicks on when I flip the switch. I will go check the rubber hose.
Old 03-07-2011, 09:05 PM   #4
Rubber hose was clean and ran a pipe cleaner through it. Reattached and turned on gas; turned on electric. Flue fan kicked on, but still get the flashing red light for failing to close.
Old 03-07-2011, 09:07 PM   #5
AKA HVACTECHFW
not, clean the hose, but the port on the motor that the hose connects to.
IT IS WHAT IT IS
The Following User Says Thank You to hvactech126 For This Useful Post:
sM319 (04-22-2011)
Old 03-07-2011, 09:09 PM   #6
biggles's Avatar
when you see the smaller fan motor running that is the stat calling in the heat the switch with the tube going to the fan is to proof of Induced Draft ..the switch closes and then the pilot,burner,supply fan should follow.for any reason the tube the switch or ID itself fail the burner will shut down..remove the tube from the fan and lightly blow into it you will hear a click could be moisture or even a bug blocking it...always check the outside tubing after heavy snow to see its clear good habit to get into...
The Following User Says Thank You to biggles For This Useful Post:
sM319 (04-22-2011)
Old 03-07-2011, 09:33 PM   #7
This is inside the house,,,,no snow, at least not much here in Texas
Old 03-07-2011, 09:40 PM   #8
Blew into both ends. Ran pipe cleaner into port on motor. It went in the length of the port. Should it have gone in farther?
Old 03-07-2011, 11:13 PM   #9
AKA HVACTECHFW
look in the port. also check for obstructions in the flue.
IT IS WHAT IT IS
Old 03-07-2011, 11:24 PM   #10
how
Rewards Points: 1,102
Just a few more thoughts.
Attach one end of the hose to the pressure switch and blow very gently into it.( Too hard and you'll wreck the switch) you should hear it click on & off. If you can't hear it doing that then try a paper clip to see if any debris is stuck in the port entry of the pressure switch.
Bear in mind that anything that limits the air flow through the burner and venting system can also cause that code. Restricted venting, reduced vent motor-turbine output, improperly sized venting, or poor electrical connections to the pressure switch, or even a faulty mother board.
how is offline   Reply With Quote
The Following User Says Thank You to how For This Useful Post:
sM319 (04-22-2011)
Old 03-08-2011, 04:54 AM   #11
An old Tradesmen
Rewards Points: 6,480
Check for obstructions in flue pipe. Could also be a bad switch.
The Following User Says Thank You to beenthere For This Useful Post:
sM319 (04-22-2011)
Old 03-08-2011, 09:08 PM   #12
Got it fixed. Pushed a little harder in the neck and got through the obstruction.
THANK YOU for your help!!!
Old 04-22-2011, 12:55 PM   #13
Thanks !! Worked for me also! Saved me about $100.00 for a service call.
Really appreciate the help/advice from everyone.
sM319 is offline   Reply With Quote
Pressure switch error phoneman77 HVAC 5 11-15-2010 06:45 PM
Carrier pressure switch test spider18 HVAC 2 11-03-2009 05:51 AM
Pressure Switch, Draft Inducer, Burner Box, Problem majorapus HVAC 7 10-25-2009 07:14 PM
Could a failed condensor fan raise pressure/trip high pressure limit switch? (Rheem) hennyh HVAC 6 07-30-2009 03:04 PM
Pressure Switch Problem? jamespappin HVAC 1 10-28-2007 03:32 AM