Pressure Switch, Draft Inducer, Burner Box, Problem - HVAC - DIY Chatroom Home Improvement Forum
Old 10-23-2009, 07:30 PM   #1
Starting last week, sometimes when I come home I hear that my furnace is not running properly. I have a york 92 efficiency furnace. The draft inducer just runs and nothing else happens. The LED indicates "Pressure switch stuck open".
Using a volt meter I measure 25 volts from one terminal to ground, and 0 volts from the other terminal to ground. There are two tubes connected to the pressure switch. One connects to the draft inducer. The other to the burner box.
I disconnected the hoses from the draft inducer and the burner box. If I suck on the draft inducer hose I hear the pressure switch click and the volt meter reads continuity through the switch. If I blow on the burner box hose the pressure switch clicks again. The pressure switch appears to be working.
When I walk outside (while the draft inducer is running) I can feel suction on the intake pipe and a draft out of the exhaust pipe. I removed the curved PCV prieces from the intake and exaust pipes so I could look down them with a flashlight. The pipes look clear as far as I can see (8 ft) before they bend.
The exhaust pipe is made up of 2 sized pipes. The smaller diameter connects the furnace up to the larger diameter which is outside. The larger diamter has become home for a pool of condensation. But because the pipes are different diameter, the water level is lower than the smaller pipe, and the smaller pipe is dry.
I have checked my condensation hose, it appears clear. I've checked the draft inducer pressure tube and the burner box pressure tube, those are fine too.
If I turn off the furnace and turn it back on the draft inducer immediately starts up. If I remove the tubing from the draft inducer, leave it connected to the pressure switch, and suck on it, the LED blinks green (I then shut the furnace off to prevent the ignition cycle). If instead I leave the draft inducer pressure tube connected, and disconnect the tube connecting the burner box to the pressure switch, the LED blinks green (no blowing in the tube required.)
When the draft inducer is on I can feel suction from the pressure tube. I can feel the burner box blowing air out of its pressure tube.
Everything by itself seams to be working, when I put it all together it wont turn on.
Is the pressure switch too stiff? Is the draft inducer not producing enough draft? I'm not sure what the burner box tube is for exactly, what does it indicate that removing it solves the problem?
majorapus is offline   Reply With Quote
Old 10-23-2009, 07:47 PM   #2
GC/Master Plumber/Mech
Rewards Points: 560
The problem here is that just blowing into a hose and feeling a suction on a hose really does not mean anything.
These pressure are measured in inches of water column.
What you may be looking at is the inducer is operating fine but your heat exchanger may be cracked.
The best way is to measure the actual positive and negative pressures with a manometer
I would ask you to call a pro because checking a exchanger is not a DIY project
You may just have a bad pressure switch but with a dual pressure switch it is best to actually measure the pressures
John Wayne once said "Life is tough and it is even tougher if you are stupid"
Tempstar and Trane Dealer
Old 10-23-2009, 08:30 PM   #3
Hvac Pro
yuri's Avatar
Rewards Points: 2,260
And now that you sucked and blowed on the pressure switch it is damaged/no longer accurate or safe/diaphragm is stretched or damaged. You need a new pressure switch for safety reasons and the unit checked with a manometer to measure the DIFFERENTIAL pressure across that switch. Rating for the switch in "WC must be known also. The pressure switch measures and proves the draft thru the heat exchanger needed for proper combustion. Not enough draft and you can get CO poisoning and overheat and warp and damage the heat exchanger/flame rollout and other very dangerous events. Your heat exchanger may be damaged/cracked and the whole unit needs checking by a York tech or seasoned Pro.
Old 10-23-2009, 11:03 PM   #4
Houston204's Avatar
Rewards Points: 556
A condensate furnace will lockout on pressure switch when the drain is restricted. You should never suck or blow into a pressure switch, it is probably damaged now.
Houston204 is offline   Reply With Quote
Old 10-24-2009, 01:26 PM   #5
A service man came out to look at my furnace. He showed me that the draft inducer was creating 1.5 in h2o pressure. He said it should be creating at least 3. So he is going to order a new part and bring it out when he gets it. He also said that the pressure switch was okay (I told him I blew into it).
Does all of this sound fair?
Old 10-24-2009, 01:43 PM   #6
Hvac Pro
yuri's Avatar
Pressure switches are never okay to blow into as they are delicate items. Someday it will fail (Xmas or New Years Day) and you may be sorry. Lots of people blow into them as they don't know what can happen, your choice whether to keep it. It is also a safety device and if it fails to shut down the burner dangerous problems can occur. LOTS of techs don't think about safety or LIABILITY but I sure do. Without knowing what part he is ordering we cannot say if he is correct. I assume it is the inducer fan itself.
Old 10-25-2009, 06:10 PM   #7
Should the draft inducer be generating more than 1.5 in h2o pressure? He said it should generate 3.0 in h2o, does this sound right?
Old 10-25-2009, 06:14 PM   #8
Hvac Pro
yuri's Avatar
If it has a "WC rating stamped on the pressure switch read it. Otherwise it would have to be read from a service manual.
Pressure switch stuck open? 2 areas im looking @ 1001miles HVAC 42 12-03-2012 03:51 AM
Home water pressure problem ATLdrew Plumbing 13 04-24-2009 11:17 AM
Tempstar pilot not lighting after draft inducer replacement Kdavid HVAC 53 03-27-2009 02:10 PM
Pressure switch stuck SStein HVAC 3 01-24-2009 03:26 PM
New Pressure Switch -- low water pressure chach Plumbing 4 01-18-2009 09:50 PM