Pressure Relief Valve Is Leaking On Boiler - HVAC - Page 5 - DIY Chatroom Home Improvement Forum
Old 10-26-2011, 06:04 AM   #61
Rewards Points: 1,216
You probably should have replaced the auto fill valve as referenced back some 50 posts ago, by the looks of that valve and the aggravation you have been going through is it worth it? A new valve is cheap as is a new expansion tank with an air separator and auto air bleed. Even if your system is old and needs replacement, in the near future you could have kept the fill valve with the new expansion tank. For less than $100 you could have done all this and still can. Not trying to make you a parts changer but sometimes things just need to be replaced.
COLDIRON is offline   Reply With Quote
The Following 2 Users Say Thank You to COLDIRON For This Useful Post:
newtech (10-26-2011), wlmpdiycr (10-26-2011)
Old 10-26-2011, 10:19 AM   #62
I will turn off expansion tank, drain the expansion tank and open the union on the pipe going to expansion tank from the boiler to let in air while draining. (No venting cap on expansion tank)
If PSI falls below 12, while draining tank, I will turn water to boiler back on to refill to 12PSI, then shut the water off again.
Then open expansion tank and turn boiler back on.
If this works/ even if it doesn't. I will purchase a new auto fill valve and expansion tank to put on. Found out the boiler was put in 20 years ago and it won't hurt to have these new parts.
After turning boiler back on, should I bleed radiators to make sure they still have water in them?
Last night they were hot, except one, it was warm (on second floor).
wlmpdiycr is offline   Reply With Quote
Old 10-26-2011, 10:26 AM   #63
What is a good brand expansion tank? The place I get parts from sells Extrol Boiler Expansion Tanks by Amtrol, in in a 2, 4.4 or 7.6 gallon. How do I determine what size tank to buy?
Old 10-26-2011, 03:29 PM   #64
An old Tradesmen
Rewards Points: 7,768
Amtrol is good.
PS: Don't worry about boiler pressure while draining the expansion tank. Adjust it after you reopen the valve to the tank.
Old 10-26-2011, 04:23 PM   #65
newtech's Avatar
Rewards Points: 164
Leave the water off until the tank is drained. Very common to see a lower pressure while draining the tank.
You need to drain the tank, let it sit to get the air in the tank. No air or not enough air will give you higher pressures.
When this is done then you can open the valve to the tank and then turn on the water to the prv. Then it should stop at around 12psi.
If not then maybe it is better to call a pro to check it out.....
newtech is offline   Reply With Quote
Old 10-26-2011, 05:00 PM   #66
Look on line for the tanks you listed there should be a tank sizing calcular that will ask you several questions, IE: gallons of water in system, temperature ranges, pressure ranges then it will give you the size tank you need.
H2O pressure temp valve leaking amiso Plumbing 1 08-11-2011 11:44 PM
pressure relief valve matt426 Plumbing 0 10-07-2010 08:50 PM
Water heater pressure relief valve confusion Flt_Simulation Plumbing 4 07-11-2009 10:02 AM
How do I install a pressure relief valve in a freezing area terryplys Plumbing 2 04-10-2009 07:31 AM
Filling a Cast Iron radiator system insulatorpro HVAC 7 10-06-2008 11:31 PM